Hoping you guys can help confirm the diagnosis of a fault before I call a plumber.
I've lost heating to the upstairs zone on my heating sysem.
System boiler is working fine feeding two other zones and the hot water.
The zone is connected via a Nest, which is saying its calling for heat but isn't translating into anything.
The same Nest is controlling the hot water and that is fine.
I've checked the voltage from the Nest through the wiring centre and up the the two-port valve for the zone and all seems sound. The valve is powered, the switch-live energizes when the Nest calls for heat, however no activity on the valve.
If I manually open the valve then it energizes one of the cores which triggers the boiler correctly.
Am I right to assume this is a faulty two-valve or could it be something more complicated?
Its a Flomasta 8982G and has been in for 3 years.