Went to this on Friday last week, boiler going to flame failure and no further on both CH and DHW. Fan running, No ignition, checked APS manually and boiler fired straight away.

Replaced APS and still same fault, owner told me there had been a lot of work in that part of the house (its a recently added unfinished extension) and the appliance had been inundated with dust and debris.

Still the boiler would light manually using the APS but on it's own went FF. Dismantled the flue, sec heat ex, and hoovered all out thoroughly, at that point my apprentice snapped the pipe spigot off the venturi so I bought a new one (£5 luckily) and fit the whole lot back together. Boiler fired up all great, job done.

Call today boiler going to FF again, this time on CH and DHW. With either demand it ignites, gas valve modulates ok for about a minute, then boiler knocks off, after about ten secs FF lights then after another ten secs boiler relights. No 'Reset' needed. If the demand is for DHW then when the burner goes off both the pump proving switch and the DHW switch remain ''on''. I'm suspecting something very simple but have checked thermistor, OH stat, Flue stat, all seem to test ok. Not convinced it's still a flue issue but wondering if anyone has experienced this. Flue is about 18" in length and has the flue pluming kit fitted.....Anyone any ideas ??? Thanks in advance.

Just to add, the boiler was moved from one side of the room to the other about six months ago and since the move the owner says it has gone FF now and again, before the move it was fine.
 
Last edited:
fans probably the culprit,especially if its a long run or plume kit fitted,it may appear to be working fine,but drops off just enough to cause this fault and the aps to drop out
 
Just one last thing, is it possible to test the pressure pulling through the fan to prove this. ?? If I use a manometer or my FGA and push the black pipe on when the fan starts could I get a reading to prove this. I've read before about proving APS's but never done it.
 
Just one last thing, is it possible to test the pressure pulling through the fan to prove this. ?? If I use a manometer or my FGA and push the black pipe on when the fan starts could I get a reading to prove this. I've read before about proving APS's but never done it.

not personally done that,would need to speak to baxi to confirm fan speeds
 
fans probably the culprit,especially if its a long run or plume kit fitted,it may appear to be working fine,but drops off just enough to cause this fault and the aps to drop out

Had similar problem on same boiler and it was the fan, as gasman said it seams to be working ok but will be tiring especially on long flues.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Potterton performa 24 eco HE faults" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread starter

goz666

Gas Engineer
Joined
Location
North West

Thread Information

Title
Potterton performa 24 eco HE faults
Prefix
N/A
Forum
UK Plumbers Forums
Start date
Last reply date
Replies
6

Thread Tags

Tags Tags
potterton

Thread statistics

Created
goz666,
Last reply from
shaky,
Replies
6
Views
266

Weekly or Monthly Email Digest

Back
Top