Currently have 14Mx15mm run from combi to tap dhw. If I replaced the last 6M section with 22mm pipe would this help? Taps closer to boiler have no problems firing the boiler.
 
Some Combi‘s have a Venturi which can affect hot water delivery. What actually happens when running hot water for the furthest outlets?
 
Some Combi‘s have a Venturi which can affect hot water delivery. What actually happens when running hot water for the furthest outlets?
What actually happens is we get no hot water. The pressure from the hot tap seems too low to fire up the boiler. I'm asking will changing to 22mm from 15mm for the last 6M help increase the demand on the boiler?
 
It’s flow rather than pressure.

Could be partially blocked aerator on tap. Remove and clean if you can. Test with aerator off.

Is it thermostatic? Could be dodgy cartridge allowing cold through when it should be hot. If cold coming through, then boiler doesn’t know to come on.

Disconnect tap connections under tap, run hot feed into a bucket and see if boiler comes on.
 