Have a Halstead Ace High boiler and enclosed combi circuit problem

I I up the pressure to 1 bar and leave boiler shut off overnight it is still 1 bar in the morning

When the boiler runs the pressure goes up to 2 bar or over After the thing has run a while and it shuts off on the timer the pressure drops to around 1/2 bar

My question before I start ripping up floor boards - is it always a leak in the pipework?

Any comment or advice appreciated

pete
 
Hi pete ... floorboards are your last resort IMO 🙂

Are you gas safe registered? Compitent? know a bit here and there ... lol?
 
Definitely no water coming from PRV pipe outside? Would get boiler checked out first.

If all ok then must be a system leak and may have to start lifting those boards.
 
Sounds like a boiler fault not pipes, if only when it's running expansion vessel is favourite for causing that what you,v described. Get a GSE mate.. Leave ya boards for now. (Gas safe Engineer).
 
It dose sound like your expansion vessel,s gone and releasing through the Prv,,
like Steve said, new Prv and check/recharge expansion vessel.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Pressure Dropping on Combi boiler circuit" which is posted in Boiler Advice Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
peterx666,
Last reply from
Brendan Rodgers,
Replies
7
Views
1,511
Back
Top