I see in this table it is below 100mb so MOP x 2.5

Screenshot_20181218-230626_Chrome.jpg
 
You need to find out the Mains pressure before the Governor that controls your installation pressure. Cadent will tell you what the supply pressure is in that area. If you get that, I can look in IGE/UP/1 and tell you the pressure you need.
 
  • Agree
Reactions: ShaunCorbs
Must be a nightmare.

To be honest, Cadent would of had it but it is not there area. It is SGN.

I have found this info though...

Going from that info it is what you have suggested and 75mb for low

Screenshot_20181219-093110_Chrome.jpg
 
There you go mip 75 mbar

Mop 23

So test would be 82.3 so 83mbar so you could test the mdpe at 100 mbar


Thanks for the calculations. As I don't have a gauge that does 100mb, I could do this as you suggested in the 1st place to 1 bar as it is only a soundness test after all. But, as you say it is commercial so should I avoid.

Well if one thing that comes out of this I have learnt a bit about cost of fittings for this size pipe and strength testing.

Thank you all
 