Hi Rautospoon,
As asked by fuzzy, where do the header tank feed and vent pipe connect to the system? A photo of those would help... It is there relative position in conjunction with the pump that determines pumping over issues!
Regards the pump pointing down over ... Just bad practise IMO.... Any large amounts of air tend to stop circulation as the impeller spins freely moving nothing!
Regards the radiator ... It will work but is piped wrong and will reduce circulation through your boiler!
Regards your boiler .... it cannot be fitted to a sealed system or combined feed and vent system. However in the instructions you can fit a 'surge arrestor'. Seen it done a few times Hopefully this image will help you understand what I'm talking about if it uploads okay

As asked by fuzzy, where do the header tank feed and vent pipe connect to the system? A photo of those would help... It is there relative position in conjunction with the pump that determines pumping over issues!
Regards the pump pointing down over ... Just bad practise IMO.... Any large amounts of air tend to stop circulation as the impeller spins freely moving nothing!
Regards the radiator ... It will work but is piped wrong and will reduce circulation through your boiler!
Regards your boiler .... it cannot be fitted to a sealed system or combined feed and vent system. However in the instructions you can fit a 'surge arrestor'. Seen it done a few times Hopefully this image will help you understand what I'm talking about if it uploads okay