Hello experts!

Having just acquired my first property this is my first post on here. :waving:

I have recently purchased a 1985 build 4 bed home. I plan to carry out some modernization work in the property. The first job on the list is to get rid of the existing Potterton boiler (image attached) and tank and put in a new Combi. I also plan to change the location of where the boiler is. It currently sits in the kitchen by one of the cabinets and I plan to have the combi installed in the dry room upstairs. Choosing the boiler seemed to be a tough one as it is however I have circled out on 30kw/32Kw Worcester or Vaillant and will be finalizing one of the two after a bit more research. They both are on par pretty much I understand.

Now here is my main dilemma. I got 4 gas engineers over to give me a quote and look at the boiler/central heating system. From what I understand I have a microbore central heating system (dont exactly know what that means) and the pipes connected to all radiators are 8mm (cheap ones Ive been told). The piper by the boiler are a different size too. 2 of the engineers said it needs upgrading to 15mm and all the pipework needs changing. The other 2 said it was ok to continue using the 8mm as it was and then one of them said they would do some sort of a service once the new boiler is installed. I'm left confused!!! :banghead:

I am thinking 10-15 years down the line and am not sure what is the best way to go about this. One of the engineers who advised to keep the existing pipes as they are said to do this because of the way the house was constructed. He said removing the flooring may pose a risk of the flooring becoming squeaky after the pipe installation because of the material used to make the flooring (upstairs). The downstairs has a concrete base under the flooring I believe so it would involve a lot of work. The mains and meter are inside a door by the main door outside the property (dunno if that helps). I mainly wanted to modernize the look of the property and am desperately looking for suggestions. Can the existing pipes that go into the floor or wall/skirting he hidden in any way? Also, mainly can I continue using the 8mm pipes for the central heating?

Looking for some expert suggestions. All your inputs will be greatly appreciated. Thanks in advance.

Cheers
K
 

Attachments

  • IMAG1887.jpg
    IMAG1887.jpg
    92.8 KB · Views: 86
Last edited by a moderator:
best to get rid of the 8mm and up it to 15mm if you have more than one shower your best option is to look at an unvented system and you can remove floor boards/planks and refit with no squeaks
 
837 will cope with a main bathroom & ensuite surely... That's what these big Combis are designed for I thought
 
flow rate of 15lpm at 35dc bit low 7.5lpm per shower

Only when both are being used at once... Most people use them accordingly, obviously if there is a high chance of multiple showers being operated at the same time then maybe unvented cylinder but this is a much bigger space requirement...
 
  • Like
Reactions: 1 person
Only when both are being used at once... Most people use them accordingly, obviously if there is a high chance of multiple showers being operated at the same time then maybe unvented cylinder but this is a much bigger space requirement...

+1 op have a look at glow worm ultracom 35 store if you have the space 19.7 lpm at 35dc
 