A

abar121

Need some help here, tried many things but still have one radiator at home that is cold. It was working ok last winter, perhaps not quite as hot as the others.

Tried:
1. Bleeding radiator, no air present. Plenty of water pressure.
2. Thermostatic valve. Moving freely and fully open. Now replaced with bidirectional valve.
3. Lock shield valve. Open.
4. Balancing radiators, tried closing the lockshield on all other radiators, but again, no flow through this radiator. Both pipes are cold.
5. Flushing with Sentinel X400. I left it in for a week, then flushed the system through. Also repeated this with another product. Water now flushes clearish.
6. Removing rad, flushing through with hose. Done, water ran through fine.
7. When re-filling the system, water passes through the return pipe fine. Nothing coming out of the feed / hot pipe.

Given number 7 above, I'm thinking that the feed pipe is blocked. It's 15mm plastic pipe unfortunately laid under a concrete floor.

Need some advice on what to try next. I was thinking of trying to back flush the feed pipe, with mains pressure.

Also, would the boiler trip out if all other rads where turned off at the lockshields? It doesn't seem too.

It's a conventional Vailliant bolier, with a megaflow style heat exchanger. High pressure mains.

Thanks,

Alan.
 
You say you have nothing coming out the feed pipe (flow) and that its plastic under the screed
Is it just feeding this rad? can you access the pipe before it goes into screed?
If so drain back down, cut pipe before it enters screed, mains pressure hose on pipe and try and push blockage through and out the flow valve, if this or none of the other ideas work, then you'll need to repipe the rad
 
You could try a wet vac on the flow see if you pull the blockage out.

Thanks. I will try and get hold of one. Got to be worth a shot.

Thanks. I'll give it a try. Are there any attachments for the vac that could help connect it up?
 
Last edited by a moderator:
You say you have nothing coming out the feed pipe (flow) and that its plastic under the screed
Is it just feeding this rad? can you access the pipe before it goes into screed?
If so drain back down, cut pipe before it enters screed, mains pressure hose on pipe and try and push blockage through and out the flow valve, if this or none of the other ideas work, then you'll need to repipe the rad

Yes this pipe just feeds the cold rad. The only other access is at the manifold which is mostly set in concrete. Also it is hard to identify which pipe feeds thus rad, at the manifold.

Thanks Alan
 
Thanks. I'll give it a try. Are there any attachments for the vac that could help connect it up?
 
7. When re-filling the system, water passes through the return pipe fine. Nothing coming out of the feed / hot pipe.
Have you removed the valve when testing for flow?
 
Yes this pipe just feeds the cold rad. The only other access is at the manifold which is mostly set in concrete. Also it is hard to identify which pipe feeds thus rad, at the manifold.

Thanks Alan

I've found a few blocked at the manifold before only way to clear was cut it out.
 
7. When re-filling the system, water passes through the return pipe fine. Nothing coming out of the feed / hot pipe.
Have you removed the valve when testing for flow?

Yes. I'm going to get some plastic pipe and bypass the radiator and see if the pipe heats up. I want to be sure the rad isn't still partially obstructed.
 
Ok I just bypassed the radiator with some fastfit.

The after running the CH the pipe is still cold. Damm. With the system still pressurized, if I disconnect the temporary pipe and open the hot/in rad valve, about half a cup full comes out, then a trickle.

What would be worth trying next? Vac or any chemicals that might work? Or would a powerflush help?

Many thanks, Alan
 
if its the last rad on the system could poss be a fault with the pump , might not be big enough or speed turned down
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Radiator cold. Feed and return pipes cold. TRV replaced, please help." which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
abar121,
Last reply from
1sammyj,
Replies
13
Views
8,182
Back
Top