I have bought a new radiator as replacement for old one.


After installation by plumber, the new radiator is heating up only to 1/3 of high. The rest remain cold.
Also, radiator is making quite loud noise when heating up.

The system/radiator is free of air.

My plumber was wondering if it may be a directional type of radiator, but he could not find any additional info in manual or any labels or arrows on radiator itself.

It looks like it it vertical type that can be installed horizontally.

Any suggestion, what can be a problem please?

Maybe someone from forum have already installed this model?


I am not a plumber, by my thoughts are it may be a wrong connection or baffle?

Any suggestion really appreciated.
 

Attachments

  • 617O+FBXskS._AC_SL1000_.jpg
did it come with the bleed / seal nut fitted, if not has it been hung upside down,
i"ve only fitted 4 of these and they have had stickers on saying in, out,
 
You might the look of that, but it has no fins. The claimed output is 6557 BTU but at T60. A mean radiator temp of 80 degrees is crazy hot.

Installed on a new system, designed to regs for flow of 55deg return of 35deg, this radiator would put out 2255BTU, or .66 kW.

B2-EN442 states all hydronic radiator and towel rail outputs are tested and presented at Delta T 50° or ΔT 50°. So an illegal advert in Amazon.
 
You might the look of that, but it has no fins. The claimed output is 6557 BTU but at T60. A mean radiator temp of 80 degrees is crazy hot.

Installed on a new system, designed to regs for flow of 55deg return of 35deg, this radiator would put out 2255BTU, or .66 kW.

B2-EN442 states all hydronic radiator and towel rail outputs are tested and presented at Delta T 50° or ΔT 50°. So an illegal advert in Amazon.
What does it mean for " no plumber" please?
 
as far as i know, no. got to be the right way,
did you follow instructions on page two?

got to go out work rang
Think he is trying to say that if horizontal you have to remove the blank that will be in the end pipe as it won’t flow it is there for when it’s vertical to assist the flow up to the top and carry on with its convection. Look at page 2 to confirm
 
We had a job where the customer had a similar issue. In the end we just knocked the baffle out with a length of threaded bar and hey presto they worked perfectly! I think the baffle is there for vertical fit to direct the water round.
 