ive just changed the 2 port on the heating side as I thought it was letting by as all rads started to get hot when only water on demand.

Fired up boiler on demand for water once changed 2 port, flow pipe to rads underneath 2 port stone cold but rads still warming up at a slow rate.

Checked bypass and it's fine. I put 10 replacement rads a couple months ago and when heating on demand all heat up nicely.

Heat only boiler, unvented cylinder.

**update**
I've just noticed it's the return pipes from rads heating up when hot water is on

Any suggestions? Blockage somewhere?
 
Last edited:
I wonder if the old rads had unidirectional TRV's (if they had TRV's) which prevented this reverse circulation? Now you have new rads in with bi-directional valves the problem has been able to show itself?
 
I wonder if the old rads had unidirectional TRV's (if they had TRV's) which prevented this reverse circulation? Now you have new rads in with bi-directional valves the problem has been able to show itself?
Good point!! I'm gonna try pop back today so I'll see if I can get a butchers at the return path and order of the heating, water and bypass.
 
Good point!! I'm gonna try pop back today so I'll see if I can get a butchers at the return path and order of the heating, water and bypass.
So the order after the pump is:
DHW, Heating, Bypass
Should be:
Bypass, DHW, Heating. Same order on return. But return pipework is concealed.
That right?
 
Yes, KingDoey has it right. The original installer didn't follow the 3 tee rule. DHW last connection before boiler. This diagram shows you what happens when you tee in the DHW return before the Heating circuit. I reckon that's what you've got going on and it has only shown as a problem with your new bi-directional TRV's.
http://www.hertsboilers.co.uk/tech/backflow.jpg
 