No just one on each is grand, you only want to stop the flow through each rad.So close off both the TRV and the lockshield on the other three. Okay.
Don't think Greenstar 30i goes below 8kW?Its the heat demand and the boiler minimum output that determine cycling or not.
The return temp to the boiler shouldn't make any difference to the boiler output or cycling time for the same heating demand, if you had 4 rads of total output of say 6 kw with a return temp of 50C (from 70C) then (assuming the boiler can modulate to 6kw or lower) the flowrate through the boiler is 4.3 LPM and the boiler deltaT is 20C giving a boiler flow temp of 70C.
if a ABV opened to give a flowrate of say 4.3 LPM (at 70C) you will now have 4.3 LPM at 70C mixing with 4.3 LPM at 50C resulting in a return temp of 60C but the flowrate through the boiler is now 8.6 LPM resulting in a boiler deltaT of only 10C but the boiler flow temperature will still be 70C..
That is also a reason for installing ABVs, to give a reasonable boiler Hx deltaT.
you could just put a bit of tape on the copper pipes, try black/white or something near the rad colour.
Even if you can't take the temps you might consider watching the boiler cycling on/off with those 4 rads on and note the on and off times for say two complete cycles, then do the same with that one rad only, if you feel like it, you would have to close one valve on each side of the other 3 rads to achieve this.
So, I've placed black electrical tape onto the two 22 mm pipes under the boiler and that has made a substantial difference when taking the temperatures. I let the boiler run for 40 minutes before taking any temperatures.
Firstly, with just the one radiator in question switched on. On/Off below refers to the "flame" symbol coming on or off on the boiler screen. Boiler temperature on-screen ranged from 48 C - 67 C. So, on average it's turning on and off every 2 Minutes & 25 seconds.
The flow/return at the rad was 45.8 C and 40.6 C (I also used black electrical tape here).
Time:
0:00 On
0:02 Off
0:05 On
0:07 Off
0:10 On
0:12 Off
0:15 On
0:17 Off
Below are temperatures I was getting on the flow/return under the boiler at various intervals:
50.9 - 39.4
47.0 - 40.9
45.2 - 37.9
61.6 - 39.0
49.7 - 38.1
60.3 - 38.5
Separately below is with the radiator still on, but with another couple of rads on the same floor turned on. I left it about 40 minutes or so to allow the other rads to warm up. Boiler temperature on-screen ranged from 57 C - 67 C. So, on average it's turning on and off every 3 minutes 43 seconds..
The flow/return at the rad was 47.5 C and 42.7 C
Time:
0:00 Off
0:03 On
0:08 Off
0:11 On
0:15 Off
0:19 On
0:23 Off
0:26 On
So you're not seeing anything from the figures to indicate that it's a problem specific to the boiler. It's more likely an issue with the radiator and the window?One Rad:The boiler would appearing to be firing for ~ 40% of the time with a average flow temp of 52.5C & return of 39C, based on a min output of 8 kw (post above) then theoretically a average boiler output of 3.2 kw, even if the boiler efficiency is very low while cycling its difficult to see that rad producing its rated output, very difficult to determine anything from a relatively small heat load with a boiler with such a high minimum output.
The second test would indicate firing for 62.5% of the time so theoretically a more believable output of 5 kw with 4 rads on.
I don't think you can really do any more to figure out what the true output of that rad is.
I think OP means that is the total run time. Not sure how long it rests before starting up but it’s in the boiler program. He has a big short cycling problem because boiler is oversized and system is not balanced. Rapidly rising return temp cuts it out. He has 2 jobs, balancing all the radiators and glazing.One Rad:The boiler would appearing to be firing for ~ 40% of the time with a average flow temp of 52.5C & return of 39C, based on a min output of 8 kw (post above) then theoretically a average boiler output of 3.2 kw, even if the boiler efficiency is very low while cycling its difficult to see that rad producing its rated output, very difficult to determine anything from a relatively small heat load with a boiler with such a high minimum output.
The second test would indicate firing for 62.5% of the time so theoretically a more believable output of 5 kw with 4 rads on.
I don't think you can really do any more to figure out what the true output of that rad is.
Once more, the radiator is PERFECTLY FINE! Boiler should not be stopstarting like this at all. It is getting too much hot water in the return and cutting out. Balance all your radiators. Set boiler temp to 55 deg and see how long it runs. Slowly increase running temperature until it runs for at least 15 minutes before cutting out.So you're not seeing anything from the figures to indicate that it's a problem specific to the boiler. It's more likely an issue with the radiator and the window?
The times above are in minutes, so it's off for ~3 minutes or so before starting up again.Not sure how long it rests before starting up but it’s in the boiler program.
Presumably the deltaT figure which you refer to is data which a radiator manufacturer can easily provide if I were to ask for this figure from a different manufacturer before purchase (and hoping that the figure which they provide isn't an over optimistic figure). What sort of figure would I be looking for, ideally?the output of that rad as its measured deltaT was only 4C.
Do you think this poor modulation issue is related to the radiator/balancing, or would it be specifically an issue with the boiler?Also the shockingly poor modulation means that a min 8 kw heating demand must be maintained to allow the boiler to run continuously.
Slowing flow through this radiator will drop its average temperature by 10 degrees or so, 40 degrees hotter than the 11 deg room instead of 50 deg so 20% less heat emission but for 100% more time. If a more continuous flow is delivered through it it will emit more heat overall. OP obviously wants a new radiator but he’ll be disappointed and poorer. He’s certainly not listening to me.Seems to be a consistent 3 mins off time, certainly agree with new window but all the balancing in the world IMO will not improve the output of that rad as its measured deltaT was only 4C.
Also the shockingly poor modulation means that a min 8 kw heating demand must be maintained to allow the boiler to run continuously.
I don't want to appear that I'm not listening. Ultimately, I have no plumbing background. I'm listening to two different opinions here and, yes I can get the window sorted, but aside from that I don't know if I need a different brand of radiator or if it's just a matter of getting the system balanced or if there's a problem with the boiler? There are no boiler error messages on-screen.He’s certainly not listening to me.
Presumably the deltaT figure which you refer to is data which a radiator manufacturer can easily provide if I were to ask for this figure from a different manufacturer before purchase (and hoping that the figure which they provide isn't an over optimistic figure). What sort of figure would I be looking for, ideally?
Do you think this poor modulation issue is related to the radiator/balancing, or would it be specifically an issue with the boiler?
Presumably the deltaT figure which you refer to is data which a radiator manufacturer can easily provide if I were to ask for this figure from a different manufacturer before purchase (and hoping that the figure which they provide isn't an over optimistic figure). What sort of figure would I be looking for, ideally?
Do you think this poor modulation issue is related to the radiator/balancing, or would it be specifically an issue with the boiler?
If it helps you, I pretty much agree with John.g.I don't want to appear that I'm not listening. Ultimately, I have no plumbing background. I'm listening to two different opinions here and, yes I can get the window sorted, but aside from that I don't know if I need a different brand of radiator or if it's just a matter of getting the system balanced or if there's a problem with the boiler? There are no boiler error messages on-screen.
If your whole system was balanced so each radiator had a 15deg drop you might surprisingly be able to increase boiler flow temp yet lower return temp so increasing overall efficiency.
Thanks guys, your input is very appreciated. As I mentioned earlier the flow for this rad is definitely going into the lockshield, and ideally it should be going into the TRV (which is not bi-directional). So I'll get that sorted and then I'll get the rads balanced so they have 15 C drops.Balancing will cost you nothing, there’s a thread here on how to do it.
Thanks for mentioning the diverters, as I hadn't heard of those. TBOE (the best of everything?)IMHO, all these rads should have a diverter fitted or be plumbed TBOE.
I've just seen a picture of TBOE at the link below, and yes that is ugly.IF you put TBOE (top & bottom opposite ends)in the search box you will find a lot of info, its supposed to be the best way to plump a rad and it might but its certainly the ugliest.
I'm doing that ASAP.This will work fine if you plumb it correctly ie flow into your uni-directional trv.
Re-plumb this rad and balance your system - the report back.
For what it's worth, I've asked the radiator manufacturer and they state that the rad does not require a diverter (or have an in-built one).Would agree with above re different type of rad as there are numerous posts re the (non) performance of "tall" rads, IMHO, all these rads should have a diverter fitted or be plumbed TBOE.
It's 3 bars per column. It appeared to go up the central bar directly above the feed. Then go across the top directly across all at the top, then cascade down heating all at same time. Hopefully, that sounds ok, if not I can repeat and see if I can determine any further detail.So, is it first moving all along the bottom to the return (outlet) straight away and is this return hot first or as soon as the others start heating.
It was set to 60C though in reality it fluctuated up and down between, what was it, 55C and 67C ish as it cycledOne other query, when you took the cycling times tests with four rads and then one, what was the boiler set point temperature?.
This is a big improvement. Need to see if your lounge feels warmer now. Why have you not balanced all the rads in your home?An update: I now have the flow pipe connected into the TRV and the return to the lockshield.
I've ascertained the order in which rads heat up on that floor. After doing, I've turned all the TRVs up full and all the lockshields closed off. Then, with the rads allowed to cool, starting with the first rad on that floor, I've opened up the lockshield as little as possible but which still allows the flow through the rad. I presume this will allow the largest temperature drop possible?
By doing so, in one room I got:
a) 58.7 C at the flow end with a 6 C drop (this is a vertical rad, but not the same brand as the vertical radiator which this thread relates to),
b) 55 C at flow end with a 15 C drop, flat panel rad
b) 55 C at flow end with a 15 C drop, flat panel rad
d) the main radiator in question: 51 C at flow end with 7 C drop
I did notice, when I checked in to look at the boiler that it was no longer switching on/off every 3 minutes any more. Actually, I didn't notice it off so I'm not sure if the cycle time has increased greatly or if wasn't switching off, I'd need to check that. Any time I looked in, it seemed to be holding steady at 62 C without fluctuation.
It didn't seem to be possible to get the 15 C temperature drop. I was being very careful to open the lockshields as little as possible whilst still allowing flow.