Reducing maximum pipe length for fittings - 110mm soil pipe

View the thread, titled "Reducing maximum pipe length for fittings - 110mm soil pipe" which is posted in Boiler Advice Forum on UK Plumbers Forums.

M

Masood

Hi Gents,

A quick question to which I can't find the answer in any of my reference books or online - I know that for gas supply and flues, each fitting increases the nominal length of the pipe. I also know that for a single WC, the maximum pipe run in 100mm is 6m, with a 1 in 40 fall. What I would like to know is that if there is a 90 degree bend in that pipe, whether I can still run 6m, or is it shortened because of the bend.

Thanks in advance,
Masood
 
Sorry to jump in on your post masood, I have the same question . I have a toilet flushing into a 90 degree connector running 0.3 m to horizontal 90 straight into a vertical 90 , which drops 0.75m and travels 2m to connect with outside waste stack . I wanted to run soil pipe outside but was not allowed to as it is a listed building .
Another part of the question is would it be beneficial to have a larger slope than 1 in 40 ? I ask as outside cast iron branches run at a slope of about 20 degrees, I thought 1 in 40 was required to ensure solids were flushed away.
Thanks for any help
 
Thanks Simon. That confirms what I'd concluded -no set reduction in pipe length per fitting, but keep bends radius as big as possible. Appreciate you taking the time to reply and sharing the link! 🙂
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Reducing maximum pipe length for fittings - 110mm soil pipe" which is posted in Boiler Advice Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
Masood,
Last reply from
Masood,
Replies
3
Views
4,985
Back
Top