Remeha avanta 28c E4 error
View the thread, titled "Remeha avanta 28c E4 error" which is posted in UK Plumbers Forums on UK Plumbers Forums.
A
AideyJ
Been called out to this error tonight but I cant work out what the problem is, boiler as been installed for 2 months with no issues previously. I can see the boiler sparking but there is no flame at all.
HELP!!
Do you have the facility to 'back heel' ? Still under warranty! :rofl:
Failing that check that the gas is turned on and the meter hasn't ran out ... first thoughts 🙂
Planning on calling out their engineer tomorrow as boiler is still under warranty, only 2 months old!
I'm assuming E4 is flame detection error yeh? If so, and to save face 🙂 It may be worth checking the basics if you haven't alrady done so AideyJ 🙂
Done all the tests but I've now discovered on other forums that the problem usually lies in the ignition transformer.
Interesting to know AideyJ ... I am not familiar with the boiler you mention so wouldn't know if any generic issues... Good luck in getting to the bottom of the problem 🙂 And if you get the chance, leave your findings here for future searchers 🙂
I fit loads of these boilers and never had a problem with them, E4 code is boiler not fired up.........check gas, electrodes, and ignition transformer however if you have a spark then it can't be that, would suggest its gas related check the valve.
bob
Reply to the thread, titled "Remeha avanta 28c E4 error" which is posted in UK Plumbers Forums on Plumbers Forums.
AideyJ,
boblydon,