clockworks

My house was built in 1966 as a 2 bed bungalow. An oil-fired Aga with back boiler heated the water in a vented cylinder. The Aga was removed, leaving an immersion heater to heat the tank.
A dormer conversion (2 beds and a shower room) was done about 13 years ago by a previous owner, and central heating was installed - Worcester Danesmoor 15/19 oil-fired boiler (no mains gas in the village).

A few weeks ago, I replaced the original TRVs with an Evohome setup.

Everything works - to a degree:

The boiler doesn't have a bypass, so I've left one radiator open. I need to get this sorted.

The hot tap in the upstairs shower room is pitiful. Flow rate is 2l per minute, and it takes nearly 2 minutes to run hot. I think it's a combination of long pipe runs, and a header tank that's only a couple of feet above the tap. The flow in the kitchen and downstairs bathroom is just about acceptable.

Incoming mains flow seems good - around 30l per minute on an outside tap.

I'm considering getting an unvented indirect cylinder fitted in the garage, next to the boiler. This would be easier than trying to squeeze the new cylinder into the airing cupboard. Current tank is about 140l.

I had a plumber in at the weekend to look at the job, and he's quoted me for a 250l Centerstore unvented cylinder, 2 port valve, and an ABV for the heating circuit, as well as decommissioning the existing header tank and cylinder. He's proposing to feed the hot water back up through an existing washing machine supply pipe that's in the garage.

I have a few questions:

Is Centerstore an OK make?

Would feeding the hot water back up a 15mm pipe be an OK solution? It'll save a lot of work, but it would make the already tortuous pipe runs even longer, and I'm concerned that the 15mm pipework might be too restrictive.

Do I need a 250l cylinder, or would 190l be enough? Both showers are mains electric, so just one bath, 2 basins and the kitchen sink.
 
Hi
Center store, are fine. They are a branded one made by megaflo. It will work OK with connecting into the 15mm but, for a few hours work. I would be feeding it in 22mm from the mains and feeding 22mm hot to the nearest 22mm hot.
 
Hi
Center store, are fine. They are a branded one made by megaflo. It will work OK with connecting into the 15mm but, for a few hours work. I would be feeding it in 22mm from the mains and feeding 22mm hot to the nearest 22mm hot.
 
250 litre too big if you are on lecki showers , but if you put a 210 in that would still do a mixer shower if you ever changed it . Failing that a 180 would do a bath no problem.
As Chalked above says the center brand are good unventeds , I fit them as well
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Replace vented immersion tank with unvented indirect cylinder?" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread Information

Title
Replace vented immersion tank with unvented indirect cylinder?
Prefix
N/A
Forum
UK Plumbers Forums
Start date
Last reply date
Replies
3

Thread statistics

Created
clockworks,
Last reply from
townfanjon,
Replies
3
Views
1,958

Weekly or Monthly Email Digest

Back
Top