S Plan heating system, heating coming on with hot water

View the thread, titled "S Plan heating system, heating coming on with hot water" which is posted in Central Heating Forum on UK Plumbers Forums.

Sandeep89

Gas Engineer
Hi Guys,

Had a question about a S plan system. When customer turns on a hot water tap the boiler gets demand for heating as well and radiators heat up, the heating radiator sign (Vaillant Boiler) flashes on the boiler display screen.

Customer has said it has been like this for a year.

I have checked the 3 port valve and the spindle is totally free, when there is demand for heating with hot water tap on and also just when the heating is running on it's own.

Would I be looking at a faulty motorised valve head?
 
Yes, that's a likely possibility. I'd check the voltages at the valve head are correctly reflecting calls for heat as the first step.

If you are not familiar with using a multimeter to diagnose this sort of fault get a sparks to help / teach you how it's done correctly and safely. (Or take a training course of some sort.)
 
The boiler would only fire up once a demand has been requested, so either it’s a Combi, or you have a different fault. Check the 24v link hasn’t been left in.
 
It won’t be firing on hot water / after it’s used unless it’s constantly on hw or wired wrong also 3 port on a unvented is a nono
Landlord is adamant it was all ok whilst they were living in the house however tenants said past year since they moved in issue has been there.

With the CH off at the programmer, with a hot water tap run CH demand still kicks in at the boiler and burner comes on.

I will be going back to investigate further.
 
You sure it’s not a combi that’s been used as a sys / heat only as you would need to run a fair bit of hw off before it calls for reheat if fed via cylinder?
 
So it’s a Y plan, not an S plan. Just go armed with a multimeter and check voltages.
 
I'd expect there to be a programmer ('time switch') for the hot water. Connected in series with the tank thermostat and set so the tank is reheated for a couple of hours a day in the night.

The behaviour described in post #1 suggests that this programmer is missing or has been set to 'always on'.
 
Hi Guys,

Was away on leave. Yes system is a Y plan with one 3 port valve. So while I have been away customer got another engineer out who replaced the 3 port valve and issue still persists.

I have come back and there is a Drayton Lifestyle programmer. When the hot water is turned is selected to 'on' on the programmer and heating off at the programmer the heating kicks in at the boiler.

I checked the new valve and again the arm/lever is totally free however if I remove the motorised head from the body the arm/lever moves back and I can then put it into manual. Put with the valve connected back to the body the arm is totally free.

With the hot water on at the programmer and heating off, if I turn the cylinder stat off the heating turns off at the boiler, but when cylinder stat is turned back up heating kicks back in again at boiler.
 
20221001_113525.jpg


This is the Drayton Lifestyle programmer wiring.
 
Sounds like a wiring fault, need to fault find at the wiring center. Would double check the hot water off is actually hot water off.
 
Last edited by a moderator:

Official Sponsors of Plumbers Talk

Reply to the thread, titled "S Plan heating system, heating coming on with hot water" which is posted in Central Heating Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
Sandeep89,
Last reply from
Deleted member 120897,
Replies
14
Views
3,676
Back
Top