Matt0029

Gas Engineer
Oct 6, 2017
1,245
110
63
37
leeds
Member Type
Heating Engineer (Has GSR)
Any ideas why a sealed system with a combi could be grabbing air. The upstairs rads have air in and the system reads 3 bar cold. When the air is bleed out the system returns to 1 bar or less. It's an ideal instinct boiler basically a logic.
 
I would add cleaner but also have a look at any towel rails sometimes they can cause bad corrosion if there cheap
No towel rails. But the system is fully copper 6 years old new build. Had inhibitor in. But never flushed originally. Was drained down recently for new rad valves.
 
Have you physically checked the pressure in the system ? it could just be a faulty gauge or partial blockage in the tube , I'd suggest and good hot flush then a chemical clean and mains water flush check then expansion vessel is charged to 0.7 -1 bar add a couple of litres of quality inhibitor before filling slowly and avoid trapping air in the system even fit manual air vents on high spots if necessary. Kop
 
Have you physically checked the pressure in the system ? it could just be a faulty gauge or partial blockage in the tube , I'd suggest and good hot flush then a chemical clean and mains water flush check then expansion vessel is charged to 0.7 -1 bar add a couple of litres of quality inhibitor before filling slowly and avoid trapping air in the system even fit manual air vents on high spots if necessary. Kop
I didn't no, I just bleed the gas/ hydrogen out. Which took the system back down to below one bar.
 
Hhmm was there a smell when vented did water come out? test the water there's many Kits available and we should really be doing it . I would say it needs a clean and possibly a new vessel you may possibly get away with not doing it ? , but if you're gonna be there a day why not do it and avoid another trip later your customer only has the one bill then and just gives a bit more peace of mind you've done the job best you can. Kop
 
I like the adey products, the expansion vessel pressure should read 0.7 - 1 bar when drained of water and pumped up . Kop
Thanks the system has had some work on it new trv valves so will of been drained recentlyish. But no cleaner. I was going to try cleaner flush from all drops. And re charge vessel
 