supared1
hello all,
first of all i'm newbie (to the site and industry) and would like to wish everyone a very happy and leak free 2011, the main reason for this post is to pick your brains and hopefully get some advice, i have recently moved ino my new home and immediately checked the heating and hot water systems, i have an unvented system (megaflo) and a sealed heating system (red expansion vessel).
Now to the point, all the downstairs radiators were only warm except one which remained cold 😕 investigating i found the filling loop was left open and the pressure was up to 2.5 bar so i reduced the pressure via the bypass/overflo and switched off the filling loop, this seemed to slighly warm the cold radiator only slightly, so i switched off all the rads (lockshield) except that one to try and balance them and no luck, but i noticed that the boiler was switching off even though the therm/heating was on and the house was cold, oh and the boiler is a halstead best 50 and has no problem with hot water, its just the heating thats baffling me.
I have also noticed that there is a gate valve just above the pump and before the mid pos valve which leads to the return i'm pretty sure thats a bypass but to me it seems to take the majority of the heated water from the boiler straight back into the return.
many thanks for just reading this because i know its a bit long winded but any advice would be greatly receaved.
Many Thanks.
first of all i'm newbie (to the site and industry) and would like to wish everyone a very happy and leak free 2011, the main reason for this post is to pick your brains and hopefully get some advice, i have recently moved ino my new home and immediately checked the heating and hot water systems, i have an unvented system (megaflo) and a sealed heating system (red expansion vessel).
Now to the point, all the downstairs radiators were only warm except one which remained cold 😕 investigating i found the filling loop was left open and the pressure was up to 2.5 bar so i reduced the pressure via the bypass/overflo and switched off the filling loop, this seemed to slighly warm the cold radiator only slightly, so i switched off all the rads (lockshield) except that one to try and balance them and no luck, but i noticed that the boiler was switching off even though the therm/heating was on and the house was cold, oh and the boiler is a halstead best 50 and has no problem with hot water, its just the heating thats baffling me.
I have also noticed that there is a gate valve just above the pump and before the mid pos valve which leads to the return i'm pretty sure thats a bypass but to me it seems to take the majority of the heated water from the boiler straight back into the return.
many thanks for just reading this because i know its a bit long winded but any advice would be greatly receaved.
Many Thanks.