Replacing type 11 with type 21 and trying to get as close as to the original output as possible - should you oversize or undersize if it's not exact? I am talking less than 5% either way.

In one radator its btu was 5159 but I can either go for 4888 or 5702 - the original was a type 11 450 x 2000 and I want to replace with a type 21 500 x 1200 or 500 x 1400.
 
With an undersized radiator you would have to increase the flow temperature to get a slightly higher output, this of course would have the same affect on all the other radiators. I would oversize slightly, you can always reduce the flow rates through it to widen the delta t and reduce the radiator mean temperature and slightly reduce its output.
 
I would tend to oversize by at least 25% or more and fit TRVs, you will then get a very fast warm up and the highest possible efficiency from a condensing boiler as the return temp(s) will/can be very low once the room temps are satisfied even with a relatively high flow temp of say 75C. Also if weather compensation is installed then gas boilers can run with flow temperatures as low as 30/35C so again IMO another reason to oversize.
 
What’s the delta T for your system? Bear in mind that a lot of heating systems in the U.K. were designed around delta 60, but the current standard introduced in the last decade is delta 50. For alternative energy sources the delta T is 40 or lower.
 
A "40 deg" rad would have be oversized by a factor of 1.7 based on a "60 deg" rad and by 1.34 based on a "50 deg" rad. The 50 deg rad base is fairly european wide now i would think.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Should you oversize a radiator?" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
Justice League,
Last reply from
Justice League,
Replies
8
Views
7,828
Back
Top