Having had a bit of investigative work done on the system I thought I would update with findings such that it may be useful for anyone else with a similar issue. Despite having had my system powerflushed twice, it appears that the culprit is still sludge, only this time it found its way into the heat exchanger of the relatively new boiler unit, so while the boiler was working, the low heat transfer to the circulating water due to the fouling had two effects. Firstly it wasn't heating the water very high, hence the initial problem with lack of heat, but secondly, as the boiler input heat was OK, but it was not transferring this heat fully to the water, the boiler flue gas temp would rise and cause the unit to shut off, thereby causing an on/off duty cycle which of course would not put any heat in when it was off.
Present Magnaclean filter is on the outlet side of the boiler, so this is being switched to the inlet side to protect the boiler and of the course with the heat exchanger cleaned out, I am now getting the heat into the system.
Thanks for all the responses and help, as a result of your input it was useful in tracking down the real cause.
Cheers and a good New Year with trouble free plumbing to you all!