I have bin to take a look at a heating system thats heating the office part of a commercial building. Last year it had a boiler change, im not sure what was there before. What has been put in is an Intergas combi boiler, tank fed on the heating side, the hot water side is not connected.
1, Any intergas installers know if intergas are happy with a tank fed set up?
2, if so what vent and feed set up do they recommend?
3, what do we think the best vent and feed setup would be in this installation (apart from sealing the system)
the current set up(old pipework) has the vent on the flow and the feed on the return, pointing towards the previous boiler being a different warren of rabbits. This has ment the system does not get very hot, and its always pumping over.
Apart from the obvious questions of the poor boiler job the system has alot of corrosion. Yes the current set up of pumping over will have made matters worse but it seems that the new boiler was fitted without the system ever being flushed as required. The benchmark reeks BS also.
The system has 35mm primary flow and returns with 20 large double radiators over a large working space. I am also questioning the choice of boiler regarding pump performance also. it also has a 22m magnetic filter on the return.
poor job all round it seems.

Adam.
intergas combi compact hre 36/40 btw
1, Any intergas installers know if intergas are happy with a tank fed set up?
2, if so what vent and feed set up do they recommend?
3, what do we think the best vent and feed setup would be in this installation (apart from sealing the system)
the current set up(old pipework) has the vent on the flow and the feed on the return, pointing towards the previous boiler being a different warren of rabbits. This has ment the system does not get very hot, and its always pumping over.
Apart from the obvious questions of the poor boiler job the system has alot of corrosion. Yes the current set up of pumping over will have made matters worse but it seems that the new boiler was fitted without the system ever being flushed as required. The benchmark reeks BS also.
The system has 35mm primary flow and returns with 20 large double radiators over a large working space. I am also questioning the choice of boiler regarding pump performance also. it also has a 22m magnetic filter on the return.
poor job all round it seems.

Adam.
intergas combi compact hre 36/40 btw