As I get a couple of these to sort every year, here's a few photos of the fix method.
For those not in the know, some Eurostars with balanced flues were fitted with a faulty batch of flue gaskets. These gaskets perish over time and allow the flue gases into the air intake giving the telltale high CO readings and smoke


The way to fix is to dismantle the flue and replace the gaskets.
See photos above - Photo 1 shows the new gasket fitted to the outlet on the top of the boiler. Photo 2 shows the gasket fitted to the elbow. Photo 3 shows the elbow back in place. In this case the boiler was mounted under a granite worktop and you are looking down the flue from the outside. Where the top of the boiler is accessible, it is easier to change the gaskets by unfastening the top of the air inlet to get at the elbow in the first picture.
For those not in the know, some Eurostars with balanced flues were fitted with a faulty batch of flue gaskets. These gaskets perish over time and allow the flue gases into the air intake giving the telltale high CO readings and smoke



The way to fix is to dismantle the flue and replace the gaskets.
See photos above - Photo 1 shows the new gasket fitted to the outlet on the top of the boiler. Photo 2 shows the gasket fitted to the elbow. Photo 3 shows the elbow back in place. In this case the boiler was mounted under a granite worktop and you are looking down the flue from the outside. Where the top of the boiler is accessible, it is easier to change the gaskets by unfastening the top of the air inlet to get at the elbow in the first picture.