Good day all,
I would like to get some advise and perhaps the solution to the issues with my UFH system.
We did install UFH in an entire house and got rid of all radiators.
The system is 14 port manifold (only 12 are in use) feeding 7 zones.
Total room area is 97 m2, with the biggest zone being 37 m2 (uses 4 ports).
The volume of the system is approximately 35 litres of water. The systems output around 7.3 kW (as per drawings). System pressure is 2.4 Bar.
The system is fed by the Vaillant Ecotec 838 (reason for such high end boiler is to feed two showers at the time), with direct loop (feed and return).
The Heating Output temperature is set to 60C.
The manifold temperature is set to 50C.
The Delta T between each zone’s Flow and Return is set to 8 – 10 C dT.
The heating kicks in in the morning around 5AM and lasts until around 9AM. Then it kicks in again around 3PM and goes until 9PM (not all zones work in the same time).
Thermostats in the rooms are set between 19C and 21C, depending on the rooms.
The issues what I have are:
1. While there is “call for heat” the boiler is always on, without having a chance for performing “condensing”, until it goes into cooling (possibly cycling?) mode.
2. While boiler is in the mentioned “cycling mode” the temperature can drop down below 30 degrees C and be like that for 20 odd minutes.
3. The consumption of the gas, only for the heating, was initially around £5 per day. This got reduced down to £3-50 (equals to about 100 kW of gas daily) by turning the heating output from AUTO to 10 kW. I did try to run it on 7 kW option, but it does not produce enough heat for the all 7 zones. The Flow temperature can only be achieved of 26C on that setting. To be honest, even 10 kW is not enough to keep the all 7 zones at 50C Flow, but I am sacrificing some rooms to the others.
I am baffled. What we were sold is the “efficient” underfloor heating system. Which suppose to be far more better than ordinary CH system. While we had the central heating in place, even with all the radiators running, the consumption was nowhere near this high (measuring in the kWh).
The supplier could not suggest anything, other than to speak to the Vaillant. After speaking to Vaillant nothing was achieved either.
Reading through the forums some people suggest to install buffer tank. But no further advise is there on what exactly is required. Perhaps there is a “formula” on what size tank is required?
Please could you advise the solutions to bring at least the running costs down and bring the efficiency of the boiler, as from my understanding having it constantly running with dT of only 10C – 12C won’t do any good in the long term, never mind constant cycling.
Many thanks for reading the above.
I would like to get some advise and perhaps the solution to the issues with my UFH system.
We did install UFH in an entire house and got rid of all radiators.
The system is 14 port manifold (only 12 are in use) feeding 7 zones.
Total room area is 97 m2, with the biggest zone being 37 m2 (uses 4 ports).
The volume of the system is approximately 35 litres of water. The systems output around 7.3 kW (as per drawings). System pressure is 2.4 Bar.
The system is fed by the Vaillant Ecotec 838 (reason for such high end boiler is to feed two showers at the time), with direct loop (feed and return).
The Heating Output temperature is set to 60C.
The manifold temperature is set to 50C.
The Delta T between each zone’s Flow and Return is set to 8 – 10 C dT.
The heating kicks in in the morning around 5AM and lasts until around 9AM. Then it kicks in again around 3PM and goes until 9PM (not all zones work in the same time).
Thermostats in the rooms are set between 19C and 21C, depending on the rooms.
The issues what I have are:
1. While there is “call for heat” the boiler is always on, without having a chance for performing “condensing”, until it goes into cooling (possibly cycling?) mode.
2. While boiler is in the mentioned “cycling mode” the temperature can drop down below 30 degrees C and be like that for 20 odd minutes.
3. The consumption of the gas, only for the heating, was initially around £5 per day. This got reduced down to £3-50 (equals to about 100 kW of gas daily) by turning the heating output from AUTO to 10 kW. I did try to run it on 7 kW option, but it does not produce enough heat for the all 7 zones. The Flow temperature can only be achieved of 26C on that setting. To be honest, even 10 kW is not enough to keep the all 7 zones at 50C Flow, but I am sacrificing some rooms to the others.
I am baffled. What we were sold is the “efficient” underfloor heating system. Which suppose to be far more better than ordinary CH system. While we had the central heating in place, even with all the radiators running, the consumption was nowhere near this high (measuring in the kWh).
The supplier could not suggest anything, other than to speak to the Vaillant. After speaking to Vaillant nothing was achieved either.
Reading through the forums some people suggest to install buffer tank. But no further advise is there on what exactly is required. Perhaps there is a “formula” on what size tank is required?
Please could you advise the solutions to bring at least the running costs down and bring the efficiency of the boiler, as from my understanding having it constantly running with dT of only 10C – 12C won’t do any good in the long term, never mind constant cycling.
Many thanks for reading the above.