something i dont fully understand , if uf heating runs half or so as cold as rads how do i keep it all in one system?
what i mean is how do i keep the rads on the first floor running hot and the uf heating on the ground floor running cool?
sorry if this is obvious , ive never put in uf heating before.
 
Hi that bloke
I'm new in the game and haven't covered anything like uf heating, but I should imagine it's by a seperate zone valve and thermostat.I'm sure the more experienced chaps will be able to assist you.
Good luck.
 
something i dont fully understand , if uf heating runs half or so as cold as rads how do i keep it all in one system?
what i mean is how do i keep the rads on the first floor running hot and the uf heating on the ground floor running cool?
sorry if this is obvious , ive never put in uf heating before.
thermostatic mixing valve on the uf distribution manifold lowers temperature to nderfloor
 
As steve says the manifold will have a blending valve on which blends the return water out from the loops into the flow from boiler to keep temp down.
 
thanks guys , so , the manifold will incorporate a mixer valve? i was under the impression that i needed a 3 port mixer valve in the system somewhere.

so , the flow and return from the boiler will go to the rads first then on to the manifold?
 
Some systems, for example the uponor system use an electronically controlled 3 port mixing valve which is plumbed in close to the manifold instead of the blending valve on the manifold. it does the same job, basically once temp is up it will start to allow return water to be mixed in with the flow from boiler.
 
the other option is underfloor heating on the ground floor and either smiths ecovectors or jaga convectors on the first floor, unlike tradional steel radiators these units can run at the lower temperatures needed for underfloor heating, this means that the boiler doesnt need to work so hard to heat the first floor. I also use this type of system on heat pumps.
regards
mike
 
thanks guys , so , the manifold will incorporate a mixer valve? i was under the impression that i needed a 3 port mixer valve in the system somewhere.

so , the flow and return from the boiler will go to the rads first then on to the manifold?
not exactly the underfloor is just piped in like a large rad can be anywhere on the circuit but generally its the first rad on a seperate pair of FandR will have its own controll valve or seperate ones for each coil of under floor system mat vstill have a three way valve controlling heating and hot water seperatly
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "underfloor heating ground floor , rads on first floor." which is posted in Renewables on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
that bloke.,
Last reply from
stevetheplumber,
Replies
8
Views
2,603
Back
Top