Hi,
I just put a couple of these in:
Problem is, the mixer valve is not regulating the output reliably. eg set boiler to max (78C) and get 57C going into the UFH circuit, which is way too high - it should be regulating to 35C on MIN according to the sheet.
I'm not sure if this is a problem with my UFH circuits or that this no name valve is not upto the job. It sort of works with the boiler flow set to 55C where I run it most of the year, but I need to be sure UFH temp cannot become excessive if I turn the boiler up during the colder bits of winter.
The 2 circuits I have are:
Conservatory: about 66m JG PB 15mm pipe laid at 200mm spacing in 75mm fibre reinforced screed floating on celotex, 20m2, expected max floor output 2kW.
Shower room: about 15m pipe, 3m2, expected floor output around 300W, similar otherwise.
The seller suggested that I might want to throttle the UFH circuits with a balancing valve to try to get a 15C differential between flow and return.
I've also taken a punt on an ESBE VTA362 valve (same port layout) for £18 on ebay, really just to see if it's a drop in replacement for that one size wise and also if it works any better.
But before I go hacking around changing everything, I wanted to see if someone with experience might be able to suggest what's wrong with my setup?
Any thoughts most gratefully received 🙂
Tim
I just put a couple of these in:

Problem is, the mixer valve is not regulating the output reliably. eg set boiler to max (78C) and get 57C going into the UFH circuit, which is way too high - it should be regulating to 35C on MIN according to the sheet.
I'm not sure if this is a problem with my UFH circuits or that this no name valve is not upto the job. It sort of works with the boiler flow set to 55C where I run it most of the year, but I need to be sure UFH temp cannot become excessive if I turn the boiler up during the colder bits of winter.
The 2 circuits I have are:
Conservatory: about 66m JG PB 15mm pipe laid at 200mm spacing in 75mm fibre reinforced screed floating on celotex, 20m2, expected max floor output 2kW.
Shower room: about 15m pipe, 3m2, expected floor output around 300W, similar otherwise.
The seller suggested that I might want to throttle the UFH circuits with a balancing valve to try to get a 15C differential between flow and return.
I've also taken a punt on an ESBE VTA362 valve (same port layout) for £18 on ebay, really just to see if it's a drop in replacement for that one size wise and also if it works any better.
But before I go hacking around changing everything, I wanted to see if someone with experience might be able to suggest what's wrong with my setup?
Any thoughts most gratefully received 🙂
Tim