underfloor heating not working upstairs
View the thread, titled "underfloor heating not working upstairs" which is posted in Air Sourced Heat Pumps Advice Forum on UK Plumbers Forums.
M
maria_oichen
Underfloor heating not working upstairs, it's fine downstairs.
-pressure gauges stay at 40
-pump working
-tried restarting by pressing button on limit thermostat, but it still doesn't work
any ideas to what the problem is?
What sort of UF system is it? Does each manifold have its own pump? If there's just the one manifold doing upstairs could it be power supply/fuse on manifold control board? More info please.
Has it ever worked or has it just recently stopped working???? Reason I'm asking if new is to ascertain if it's been installed properly??
Welcome along to the forum.
Yes,this is the system, but we can't get hold of the manufacturer anymore. What is u/s? How can I check if the valve is stuck?
Thanks for your help
Here is a pic of manifold
No mixing valve fitted.!!! Must heat the floor very hot!
Make sure everthing on the system is calling for heat then On the motorised valve to the left of the manifold, there will be a manual lever. Try moving that. If that works, you need a new motorised valve
The TMV is in the correct place for a set up like this.
With a plate separating the two systems the ufh loop side should be clean as a whistle.
Well spotted!
I presumed that the plate was for hot water :32: so all the system is temperature controlled by the one tmv?
Problem will be motorised vslve then if all else is ok.
I moved the lever and it works...so do you guys think it's the motorised valve? That was last replaced about 6 years ago. How can I tell of that's the problem?
Most likely would be the motorised valve head, but. Could be the valve body. These can go stiff and burn out a new motor.
Firstly it needs checking to see if power is getting to the valve, then if it switching a live back to the pump. If all this is fine, it will need a new complete valve. If possible change it for a better manufacturer like Honeywell.
Manufacturer went bust some years ago I think. Looks like the problem is in the zone valve but as suggested see if it's actually getting a supply on to motor it open before replacing, could be lack of supply from the timeswitch or thermostat or whatever is controlling it.
Kee triple tube started up in the eighties. Know a bloke with this stuff fitted in his home and has gave him a lot of trouble. They soon went bust but not before leaving a trail of dodgy installations in their wake.
The plate heat exchanger in that arrangement with a tmv was a good design though. Especially if you wanted system separation.
And also it gave a first stage of temperature drop across the plate which could be as high as 10c.
Due to the crappy pipe they used.
Thanks guys! I thinks it is a faulty motorised valve if I keep it on menual, heat going through. As soon as I turn it back to auto the heat stop. Will order one it's was a Honeywell one.
Reply to the thread, titled "underfloor heating not working upstairs" which is posted in Air Sourced Heat Pumps Advice Forum on Plumbers Forums.
maria_oichen,
Sparkgap,