Got back there on Thursday and 2 days and £540 worth of materials later it's all safe and almost to regs.
IMG_20141002_115209794 by
Mike Jackson1, on Flickr
IMG_20141003_155416002 by
Mike Jackson1, on Flickr
IMG_20141003_155443837 by
Mike Jackson1, on Flickr
Day one I started by draining down and rectifying the wet side of the CH. Discarded the 3 port and fitted and fitted 2 new zone valves and tidied up the pipework as much as possible. I then moved onto the wiring. Took me 2 hours with a multimeter to figure out where all the wires went. The programmer had 3 3 cores leaving it, one to the mains plug, one straight to the boiler and one i could fathom where. Two of the wires went up and across the loft so I could cut them and use the boiler feed down and use the other two to give me my power and CH/HW ons to my JB. In the loft I had two wires, one coming to the pump and one to the 3 port. I couldn't fathom where these came from, I assume from a JB buried somewhere, I cut these and terminated them as I could rewire it without using them. The room stat had wires going to it but no matter what I did at the stat nothing registered at the two wires in the loft. I foitted a Honeywell RF2 pack to provide a new room stat.
Day 2, time to sort out the discharge. Firstly I needed to raise the inlet controls so that I could get a proper fall from the PRV. First issue, no drain off on cylinder. I turned the cold water off and released the pressure in the cylinder. I then held a bucket under the controls and loosened the last nut before the cylinder, nothing. I took it off and a dribble came out but nothing more. I now had a cylinder full of water held in place by a vacuum. I put the control back in place whilst I grabbed the fittings and fabricated a new inlet pipe. I took the control off and no water came out. I moved the bucket to under the speedfit elbow by the cylinder and removed it, logic told me that nothing should come out but I held my breath and had a speedfit blank ready just in case. On with the new pipework to high level and I could breathe again. Refitted the controls and re ran the cold inlet. in copper, neatly clipped across the rafters.
Now to the discharge. Inside was the easy bit, both D1s to a new tundish and CH discharge teed into D2 (not a fan of combining discharges but not a lot of choice here). Now for the fun bit, externally there was a pitched roof extension below where the discharge emerged. No way to get to it off a ladder it would have needed scaffold. Not an option here so it came down to hanging out of the window and poking a pre bent section of pipe through the existing hole in the fascia. Took me a while but I managed it, I even got a couple of clips on. The discharge now runs onto the roof. The roof is about 2 1/2 metres from the plastic gutter so not quite to the 3 metre requirement but a lot safer than discharging straight out of the fascia.
Finally I tested it all and insulated all of the pipes I could get to. The customer didn't even pale when I gave her the £1140 bill, she was just glad to have it all working safely again. If she ever comes across Dave Mamone I think she'll flatten him, she's quite a large lady. As well as making a complete abortion of the job, Mr Mamone charged her for a new pump and new valves and didn't even fit the one supplied. To make matters worse whilst the job was being done her husband was taken seriously ill and rushed into hospital so was unable to check the work.