Hi all,
This is my first post so hopefully i've put it in the right section. I'm currently working on my gas portfolio before sitting the ACS. Today I serviced ( under Supervision ) a vaillant ecotec plus 831 combi, working pressure at meter was 19.5mb but at boiler only 16mb. I queried this with supervising engineer and he said this was acceptable according to MI, I've looked at vaillant's spec and it says the inlet should be within the 17-25mbar range. Have I been given bad advice or am I interpreting the MI wrong. We had it drummed into us at college that from meter to boiler we could only accept a 1mb drop!! any advice would be great 😕
This is my first post so hopefully i've put it in the right section. I'm currently working on my gas portfolio before sitting the ACS. Today I serviced ( under Supervision ) a vaillant ecotec plus 831 combi, working pressure at meter was 19.5mb but at boiler only 16mb. I queried this with supervising engineer and he said this was acceptable according to MI, I've looked at vaillant's spec and it says the inlet should be within the 17-25mbar range. Have I been given bad advice or am I interpreting the MI wrong. We had it drummed into us at college that from meter to boiler we could only accept a 1mb drop!! any advice would be great 😕