I would like some opinions on this situation.

Vaillant Ecotec pro 28

Installed 2 years ago,

Commissioned Gas pressure reading 16.5mb at max rate.

1st annual service passed.(2018)

Just has second Service all combustion tests passed, and issued a Warning Advice notice of Immediately dangerous (ID) Reason Gas pressure on gas valve 14mbar, min requ 17mb.

Action: New 22mm gas pipe.

Vaillant Boiler installation and maintenance instructions says

Permissible gas flow pressure for operation with
G20 natural gas: 1.3 … 2.3 kPa (13.0 … 23.0 mbar)

Pressure at meter good, was checked by cadent with boiler on and all gas hobs on full.
No reply from original Gas safe installer.

Should I ask a for a second opinion on why it has classed a ID?

Boiler was switched off, but gas was not capped off.

Would it be safe to run boiler ? ( has been working fine, with no faults, good flame)

Question, Approx How much would running new pipe on outside property cost from gas meter to boiler. Metre at front if house, boiler at back of house 1st floor bedroom.
 
Depends on kw of boiler I’d be looking at some 28mm pipe there if it’s a long run. If it’s ID it should be capped off so it sounds like an indecisive engineer. You mention good flame you shouldn’t be removing the front cover of your boiler as it creates a combustion seal. It’s not just about flame picture it will also be the FGA readings, I assume he did one
 
  • Like
Reactions: Burger
You either need to provide all the evidence to the engineer that has capped it or start over again. Boiler should be capped if Classed as immediately dangerous.
 
  • Agree
Reactions: 1 person
When I meant flame good, was referring to
upload_2019-3-26_10-13-57.png

also no LF faults
 
  • Like
Reactions: Burger
How did cadent test if the boiler is off?
You can get a second opinion, they can cut a test point under the boiler to get a true reading
 
You need a gas safe registered engineer as I have already said above mate.
Thanks, I will ask them to come back and recheck. As its under a service agreement, I hope they do come back with another Engineer to re-check. Then id still low, then will need to get quotes for new gas pipe and wondering what approx cost would be?
 
As we say we don’t know distances routes or where you are in the world so we can’t comment on cost
 
  • Like
Reactions: Nkgas
You need a second opinion from a Gas safe registered Engineer who has carried out some on site tests.

The 14 mbar W.P. (Working pressure) is not something I would consider Immediately dangerous but I do not know the reasons he came to that conclusion?

If it was considered to be immediately dangerous, I would expect the Engineer to ask your permission to disconnect it from the gas supply and also issue a warning notice explaining the reason.
 
  • Agree
Reactions: 2 people
You need a second opinion from a Gas safe registered Engineer who has carried out some on site tests.

The 14 mbar W.P. (Working pressure) is not something I would consider Immediately dangerous but I do not know the reasons he came to that conclusion?

If it was considered to be immediately dangerous, I would expect the Engineer to ask your permission to disconnect it from the gas supply and also issue a warning notice explaining the reason.
The notice says " Gas working pressure at P1 on gas valve 14mbar min req, 17mbar.
Details of action taken: Boiler off, gas off. remedial action required: New 22mm gas pipe.
But thr gas is still on, so wanted to know if running at 14mbar is ID?
 
You need to get a different engineer out. 14mb is low but still within manufacturers tolerance...
 
I wasn't there to witness why it was classified as i.d. I (like anyone else) would need to carry out various tests in order to arrive at a decision. Sorry, I know this is little help and I hope you understand that as registered Engineers, it would not be fair to undermine a decision made by another registered Engineer over the internet, based purely on what you tell us. The Engineer who you dealt with may have had good reason to arrive at the decision he did.

There is a bit of conflicting information though. Above, you mention the 13 mb to 23 mb which comes from the newer manuals. The Engineer has wrote 17 mb required. That information was from older manuals so which one do you have?
 
I wasn't there to witness why it was classified as i.d. I (like anyone else) would need to carry out various tests in order to arrive at a decision. Sorry, I know this is little help and I hope you understand that as registered Engineers, it would not be fair to undermine a decision made by another registered Engineer over the internet, based purely on what you tell us. The Engineer who you dealt with may have had good reason to arrive at the decision he did.

There is a bit of conflicting information though. Above, you mention the 13 mb to 23 mb which comes from the newer manuals. The Engineer has wrote 17 mb required. That information was from older manuals so which one do you have?
I have the new one. not sure why engineer wrote down min req. 17mbar. maybe he was not aware of new values?
 
I have the new one. not sure why engineer wrote down min req. 17mbar. maybe he was not aware of new values?
Maybe not!
Best thing to do is inquire. He may well have the 17 figure in mind and be unaware that it has been altered recently.
Worth asking in my opinion, it could save an expensive job.
 
Maybe not!
Best thing to do is inquire. He may well have the 17 figure in mind and be unaware that it has been altered recently.
Worth asking in my opinion, it could save an expensive job.
Agree. I have been in touch will the call centre and they wont send another engineer until I can provide proof/paper work from candent to show that gas meter pressure was checked. Thats going to take another 5days!.
 
Agree. I have been in touch will the call centre and they wont send another engineer until I can provide proof/paper work from candent to show that gas meter pressure was checked. Thats going to take another 5days!.
Worth doing though mate to be honest.
 
  • Agree
Reactions: 1 person
Agree. I have been in touch will the call centre and they wont send another engineer until I can provide proof/paper work from candent to show that gas meter pressure was checked. Thats going to take another 5days!.
If you are without heating and Hot water because of something you think may be their fault, then you could insist on a visit?
 
Nope. I fit one when installing the boiler. As I once had 14.5 at the valve. Put a test point in before the boiler and had 19 at the boiler.
Thanks Very interesting ...

On a side note. When I requested to have the condensate trap cleaned, he put it back without filling with water. When I asked why? As Service manual says to, his reply was no need for this type of boiler, when boiler runs it will fill by it self.

Is he right?
 
Thanks Very interesting .

On a side note. When I requested to have the condensate trap cleaned, he put it back without filling with water. When I asked why? As Service manual says to, his reply was no need for this type of boiler, when boiler runs it will fill by it self.

Is he right?

No. The condensate trap should be filled prior to running the Boiler. If the trap is dry, products of combustion will exit the condensate pipe termination point until the trap has filled.

If all that you say is true, I think you should voice polite concern in writing (email) to the service manager.
 
Thanks Very interesting .

On a side note. When I requested to have the condensate trap cleaned, he put it back without filling with water. When I asked why? As Service manual says to, his reply was no need for this type of boiler, when boiler runs it will fill by it self.

Is he right?
We’re you watching, reading the book and offering an opinion during the service?
 
Valliants are known to loose pressure through the gas valve ask your GSI to install a test point before the gas valve and retest , you should have 21mbar +/- 2mbar at the meter and 20 mbar +/- 2mbar so no lower than 18mbar at this test point on full load . Kop
 
  • Like
  • Informative
Reactions: 2 people
Valliants are known to loose pressure through the gas valve ask your GSI to install a test point before the gas valve and retest , you should have 21mbar +/- 2mbar at the meter and 20 mbar +/- 2mbar so no lower than 18mbar at this test point on full load . Kop
So what I said😛😛😛
 
When he did the annual service did the engineer also open up the burner and brushed through? Has he checked the exp. vessel, flue integrity, has done all the **** ? Seems like he either was lazy and rushed the service or he has not got a clue. As @Last Plumber has mentioned if that all is true you should perhaps write an email.
 
When he did the annual service did the engineer also open up the burner and brushed through? Has he checked the exp. vessel, flue integrity, has done all the **** ? Seems like he either was lazy and rushed the service or he has not got a clue. As @Last Plumber has mentioned if that all is true you should perhaps write an email.
No, burner was not opened and brushed. exp, vessel was topped up.
**** was done with a print out.
does my gas pipe have a gas test point valve? have attached a photos.

001.JPG


002.JPG


003.JPG


004.JPG
 
No, burner was not opened and brushed. exp, vessel was topped up.
**** was done with a print out.
does my gas pipe have a gas test point valve? have attached a photos.

View attachment 37941

View attachment 37942

View attachment 37943

View attachment 37944
There is no test point installed as far as I can see. How did he re pressurise the exp.vessel ? Did he drain the boiler ? I do not mean the flue gas analysis I mean **** which are certain things to examine, gas rate, integrity of the flue, supply of combustion air,safety controls, etc...
 
  • Like
Reactions: Burger
There is no test point installed as far as I can see. How did he re pressurise the exp.vessel ? Did he drain the boiler ? I do not mean the flue gas analysis I mean **** which are certain things to examine, gas rate, integrity of the flue, supply of combustion air,safety controls, etc...
I am not sure, but this was ticked on the service check list.

005.JPG
 
P1 is the Boiler running at Max and he has tested the pressure at the valve. Shaun is right with the drop on a Vaillant in that the pressure will be higher at the appliance inlet than at the valve test nipple. Your Boiler will be three this year and I can't remember when the manual was altered but if you have the one left by the installer and it says 13 mb min, then ask them to come back.
 
The boiler also has not been cleaned as it should be done annually. He did not open the burner and cleaned and checked the electrodes. I would also say that the gas rate seems dodgy to me meaning I don’t believe he has ever done it. However, I would call them back
 
The boiler also has not been cleaned as it should be done annually. He did not open the burner and cleaned and checked the electrodes. I would also say that the gas rate seems dodgy to me meaning I don’t believe he has ever done it. However, I would call them back
It’s not required every year
 
  • Agree
Reactions: 1 person