I've just been to a house (Not a job) that has a gas bbu with a radiant fire on the front and I'm convinced that the free air isn't enough but I'd like to check with anyone that has a bit more know how when it comes to working these things out.
The unit is a Myson Housewarmer 30/45 with an unnamed radiant fire on the front. It's a lined brick built chimney btw. The room is approximately 18 feet by 16 feet and currently their's a 65 cm2 free air vent in the corner of the room that vents directly to outside.
I've worked it out like this:
45KW (Gross) ÷ 1.11 = 40.5 KW (Nett)
40.5 + 5 = 45.5KW nett total heat input
45.5 = 5 = 227.5 cm2
227.5 - 35 (Adventitious) = 192.5 cm2
There is a free air vent that states it's 65 cm2 so that leaves another 127.5 cm2 that's needed to make this place safe, or am I missing something?
Any advice on this would be great.