Hi all,
Been contacted a month or so ago by a customer who wanted their system powerflushed on the advice of a Viessmann engineer. The customer has a Vitodens-100W 35KW Combi boiler in their house. The Viessmann engineer removed and cleaned the secondary plate heat exchanger in the boiler and pulled some fairly sizeable (up to 5mm across) flakes of magnetite out of it.
We have been to powerflush the system. Here's where it gets odd! We connected the powerflushing machine up on the return pipework below the boiler (split the pipework and connected onto there). The whole system was then properly powerflushed. The boiler worked fine for about a week then the issue returned. Previously the F2 fault (circulation issue) only occurred with hot water being called for. Now the boiler is starting to cycle on central heating mode too. On looking at the boiler it is very quickly going from 30 or so degrees up to 90-100 degrees. This rise only takes a minute or so. It then cools and repeats. Because of this the furthest rads on the system are now not getting warm.
Did a customer service visit tonight. Our engineer has certainly got the system clean and I've seen no sign of any airlocks. We took samples from a couple of radiators and also from under the boiler, the water is nice and clear. Despite this, something is stopping circulation. My initial thoughts were that the primary heat exchanger might be clogged up but this isn't possible as the powerflusher would always be sending water around the primary heat exchanger. I think it's not possible this could still be blocked.
Which leaves the pump inside the boiler as the only possible problem, right? or wrong? Would appreciate any thoughts, particularly from anyone who has experience with Viessmann combis!
Been contacted a month or so ago by a customer who wanted their system powerflushed on the advice of a Viessmann engineer. The customer has a Vitodens-100W 35KW Combi boiler in their house. The Viessmann engineer removed and cleaned the secondary plate heat exchanger in the boiler and pulled some fairly sizeable (up to 5mm across) flakes of magnetite out of it.
We have been to powerflush the system. Here's where it gets odd! We connected the powerflushing machine up on the return pipework below the boiler (split the pipework and connected onto there). The whole system was then properly powerflushed. The boiler worked fine for about a week then the issue returned. Previously the F2 fault (circulation issue) only occurred with hot water being called for. Now the boiler is starting to cycle on central heating mode too. On looking at the boiler it is very quickly going from 30 or so degrees up to 90-100 degrees. This rise only takes a minute or so. It then cools and repeats. Because of this the furthest rads on the system are now not getting warm.
Did a customer service visit tonight. Our engineer has certainly got the system clean and I've seen no sign of any airlocks. We took samples from a couple of radiators and also from under the boiler, the water is nice and clear. Despite this, something is stopping circulation. My initial thoughts were that the primary heat exchanger might be clogged up but this isn't possible as the powerflusher would always be sending water around the primary heat exchanger. I think it's not possible this could still be blocked.
Which leaves the pump inside the boiler as the only possible problem, right? or wrong? Would appreciate any thoughts, particularly from anyone who has experience with Viessmann combis!