Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Install the app
How to install the app on iOS

Follow along with the video below to see how to install our site as a web app on your home screen.

Note: This feature may not be available in some browsers.

Jul 24, 2019
7
0
1
Member Type
DIY or Homeowner
We had this problem for a few days last year, but has appeared again. During these warmer temperatures that we are currently experiencing our boiler stops heating the hot water. Upto a couple of days ago when it was cooler it was working fine, and if as last year as soon as it cools off again it will be back to normal working.

Conventional condensing boiler (not combi), it does have the outside weather compensating sensor.

Anyone any ideas - I'll look into getting an engineer in over the next week, but suggestions might help point him in the right direction if these problems have been experienced previously.

JP
 
The weather compensator (WC) is intended to override the boiler outflow temperature set-point (as shown on the Vitodens panel). This is fine except in hot weather when the demand temperature (from the WC’s performance graph) is too low for hot water to reach a useful temperature. The cylinder demand box fixes this by (in effect) overriding the WC’s thermostat when DHW cylinder thermostat demands heat. As soon as the cylinder water is hot enough, the demand box tells the boiler “OK – your target outflow temperature is now set by the WC again. So in unusually hot weather – and without a cylinder demand box – the boiler may never fire to heat DHW at all.

OP does not mention which wiring plan his/her system uses (e.g. Sundial S,Y or W), but Viessmann say that WC is not possible with S-Plan. It is, vide an earlier post on this forum, but needs additional wiring and is forces the system to run ‘DHW priority’ (not necessarily bad thing).
 
Is the weather compensation adjustable? I guess that normally this would be installed in the room heating circuit rather than the hot water circuit.

If the weather compensator is adjustable, does changing the setting change the situation?
 
When weather compensation is operating, control over flow temperature using the temperature control knob on the front panel is overridden and a default ‘boiler temperature vs outside temperature’ curve is applied. Turning the knob does, however, provide some limited adjustment to the curve if the boiler temperature is consistently too low or too high, but I don’t know of any Viessmann documentation that specifies by how much the curve is shifted when the knob is in a particular position.
This is for the Vitodens 100 series; weather compensation on the 200 series is more elaborate and the installer can select one of many curves that is most suitable to the house construction and insulation.

Weather compensation is not installed ‘on the heating circuit’ – it is not like a room thermostat which reacts to the how hot the house gets – but is intended to allow earlier reaction to outside temperature changes by changing the flow temperature. How DHW (tap) temperature is controlled depends on the systems wiring plan and whether a cylinder demand box is installed (vide my 27th July post
 

Official Sponsors of Plumbers Talk

Similar plumbing topics

A
Replies
1
Views
923
UK Plumbers Forums
Deleted member 120897
D

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.