Ok, just a layman's view here. I understand fully the need for a PRD in a shower unit. I know the Physics of it all and I get how they work totally. But why nowadays is it a piddly little soft ball popping out of a hole and not a proper sprung loaded valve set to open at the same pressure the ball pops at? It is no problem to make a valve which will open cleanly at the required pressure but will reset itself if the pressure is released. We have these fitted in every car on the road in the header tank of the cooling system. If fault in the valve is considered a problem, it could even be paralleled with a soft ball type which blows at a slightly higher pressure to override the valve if it fails.

I would guess there could be a point made that the PRD blowing enforces diagnostic action to be taken as to why and a repair implemented but, in truth, will the average handyman not just replace it and trust to luck? Let's be honest, the only thing which can cause the valve to blow is blockage in the outlet pipe and head setup. That is easily spotted and fixed.

So why not fit proper valves which reset themselves when the fault over-pressure is removed? Is it purely to keep on selling PRDs? 😉
 
Last edited:
Absolutely agree with the cost idea. It never ceases to amaze me that companies still think they have to shave off every penny in order to sell a superior product. Development costs in this area are low as it is all "done technology" and is really just a repackaging of already existing parts. And I for one would definitely pay say £15 rather than £12 for a replacement part which is more or less a one off cost.

It's an oddity that nowadays a third party company hasn't gone down this route. Examples of small cheap pressure relief valves which open for a pressure event and simply close once the pressure drops are everywhere. I'm looking at plumbing types for central heating boilers, gardening types for pressure spray containers, brewing types for kegs and fermentation jars, air types for compressor vessels, they are everywhere and many cost less than the price of a replacement current one-off type. The range of pressures available is easily wide enough to include what we would need. Let's face it, it's a couple of plastic parts, a spring and a rubber washer and voila!

I can't help wondering if there must be an element of forcing the owner to address the cause before fitting a replacement which is sensible. However, how many owners simply push the ejected ball back in or fit a new sacrificial cap and just hope for the best? A diaphragm type with the diaphragm on a spring loaded clip on mechanism which blows off but can be clipped back into place would be a real step forwards. A unit with a lower pressure spring valve for short temporary issues and a higher pressure sacrificial ball/diaphragm valve override when there is a definite serious blockage is easy to design and implement and would do the job more permanently and cheaply in the long run.

I did have a thought. Looking into things recently I found that a standard electrical shower unit should not be used with a two option overhead rain/handheld type. That outlet configuration seems to be designed to only work with mixer taps fed from the hot/cold water. At least one issue seems to be that the selector knob of a two head type can be stalled in a mid position between the two heads where the flow is at least severely restricted which of course blows the valve. That is understandable as the restricted flow can't be allowed to happen with a fixed heat output electrical unit. But why not fit this type of valve to cope with that situation. The spring valve could cope with releasing enough water to keep the system safe even if the selector bridges the two. Or better, why not just design the selector to have a short blend step from one head to the other when switched?

Is this a $1M idea waiting to happen? Anyone with a 3D printer care to try it out?😁
 
Is this a $1M idea waiting to happen? Anyone with a 3D printer care to try it out?😁
More like a $1M law suit waiting to happen. Safety reliefs where failure risks injury have to be 100% fail safe, which is why they are usually burst discs or some other non-resettable design. Resettable ones need period inspection and testing...
 
More like a $1M law suit waiting to happen. Safety reliefs where failure risks injury have to be 100% fail safe, which is why they are usually burst discs or some other non-resettable design. Resettable ones need period inspection and testing...
But does failure risk injury with what I outlined? An additional lower pressure valve would not interfere with the action of the existing valve which they are happy to manufacture and sell Chuck. I'm not suggesting removing the current failsafe ball/disc type, only adding an extra layer to prevent that one shot type from needing to act at all.
 
They know about it

Triton years ago had a defective batch of balls (slightly too small and would go if the handheld was too high and with the hose being on the short side would cause a high restriction) rather than address the issue the reps back then just handed us a longer hose and new prv units was cheaper to do that instead of changing the model / sending service agents out to retrofit
 
A little more thinking made me realise that, if you made this a short Tee extension unit with a 1/2" female loose connector on one end, a male on the other and a 1/2" 90deg arm carrying a cheap PRV it will fit between the existing shower unit hose outlet and the hose itself like a short extension. It's then retro-fittable to any unit out there with a 1/2" hose! And as it is a plain straight through pipe it does not interfere with ANY safety function in the unmodded system.
 
A little more thinking made me realise that, if you made this a short Tee extension unit with a 1/2" female loose connector on one end, a male on the other and a 1/2" 90deg arm carrying a cheap PRV it will fit between the existing shower unit hose outlet and the hose itself like a short extension. It's then retro-fittable to any unit out there with a 1/2" hose! And as it is a plain straight through pipe it does not interfere with ANY safety function in the unmodded system.
Someone tested a Triton PRV , one of cheaper models,and it operated at 1.38bar.
 
Sorry for the delay in updating this discussion, I have been waiting for delivery of a simple PRV I found online. I now have the new test valve in place in the 90deg arm of a three way fitting connected between the electric shower outlet and the hose. Note that that in no way affects the original internal PRV action. All parts are in chrome so it looks a tidy and integral part of the shower unit.

As you advised my overhead rain shower unit with a separate handheld hose and head was not intended to be used with an electric unit as there is a dead spot between the two on the selector knob. This means that flow would be stopped for a fraction when switching. This is an obvious genuine safety issue if it were to be left in that no-flow position. Hence as you say all units are fitted with some form of trip valve fitted into the heater unit. But why a one shot device which has to be replaced every time it trips? My own Gainsborough heater has a ball type, currently £15 if you fit it yourself, and it had popped on the occasion I first became aware of this whole issue. I then learned of the problem and the requirement to not use this type of shower setup with an electric heater. However, if we fix this issue then surely there is no reason why not.

The new release valve is a 0.5bar metal type looking a bit like a whistle. Thanks John.G for the 1.38bar benchmark, it was a great guideline. To my eyes it works perfectly! It does not leak at all during normal use and on changeover from head to head it now gives a short spurt as the selector crosses the dead spot and it releases the pressure. There is absolutely no need to transfer with any haste, even if set fixed halfway so no water flows out of either head it easily vents enough water to not trip the internal PRV. It makes obvious sense to ensure you orientate it so it vents somewhere it can drain away cleanly, mine is onto the wall tiles and down into the bath.

I've added a pic of it in place and a vid of it working. You can see the spurt as I slowly swap from head to head. I do mean "deliberately slowly". Normal natural swapping action is much faster than this. You can see I did the changeover slower and slower to force the valve into action to show it releases enough pressure to do its job. I would welcome your thoughts on this as a solution. Remember, the original internal PRV protection is not affected in any way so all designed in safety precautions should be preserved!

 

Attachments

  • PRV_Fitted.jpg
    PRV_Fitted.jpg
    21.9 KB · Views: 30
Last edited:
If you select maximum flow, temperature control to minimum, does that 0.5bar PRV still stay closed?.
What is the shower power output?.
 
The shower is a Gainsborough 10.5 SE which has only a single temperature control with no switching of multiple elements. I do realise that the temperature is set purely by adjusting the flow rate internally so the lowest temperature incurs the highest flow rate and pressure. I have already found that when the temperature is almost all the way down, maybe only on about 20% and below, the valve does open prematurely. It isn't a huge gush, just a fair sized trickle. However, I did buy another 1bar valve exactly the same as the one I have just fitted which I will try to fit.

These valves are standard BSP fitting, (1/8"), and a few turns of PTFE tape meant they only had to be fitted hand tight to be water tight at the joint. So swapping is very easy.

As I keep a spare internal PRV on hand it won't matter too much if it blows during testing but as I said, having this system in place doesn't affect the action of that internal valve in any way, it certainly doesn't increase pressure, so it really shouldn't be needed. I did want to start with the lowest pressure valve I could source as I wasn't sure of the setting of my own model's internal valve and I had no idea of the working pressure at the outlet of the heater. As you pointed out the 1.38bar unit you knew of I took that as my starting reference. I'll fit the other 1bar valve later today when I get a minute and test that.
 
Just fitted the 1bar unit. It is definitely much better. It still drips slightly at the lowest temperature setting which is actually quite reassuring but it is now a lot less than before and only at the very lowest temperature setting. The action is exactly the same as before with full relief even when the selector is locked in the mid position and offers no flow out of the rain head or handheld head. I'm sticking with this one. The type I used can be seen here: AliExpress example of PRV. Granted this is a Chinese site and there will doubtless be some who won't buy from there but it at least shows what is available if you can find it in this country. Here is why I have no qualms buying from China direct: Amazon version. £4.40 delivered v £45.35? No contest!

Incidentally, apologies for incorrect information earlier, I said I used a 1/8" version which was wrong. It was the 1/4" version I bought fitted into a 1/2"M-1/4"F adaptor.

Of course, a penny has just dropped here, temperature plays a part in this too. Restricted flow through a blockage fault means a reduction of water flow through the heating chamber. This leads to a rise in its temperature up to potentially dangerous levels which is what we are trying to protect against. The usual ball valves have a wax interior which will melt and reduce the blocking properties of the ball allowing it to be forced through the valve emergency outlet. I have no experience of the other form but the split disc type valves presumably are weakened by increased temperature to reduce their strength to splitting. This is obviously a part of the action but again, the protection this action offers in both cases should not be compromised at all by my secondary valve.
 
Electric showers are designed to give their rated flowrate at a 1.0bar dP so not surprising that the 0.5bar PRV is lifting. All showers also have a dual temperature thermal cut out, TCO, the first (Triton&Mira) stat operates at 48C and self resets, the second, at 75C, does not reset and the TCO must be replaced.

My present mains temp is 17C.
A 10.5kW shower flowrate will have to fall to, 10.5*860/60/(48-17), 4.86, say 5.0LPM before the 48C TCO kills the power to the heating element with that mains temp. At a fairly typical 40C showering temp, the flowrate must be, 10.5*860/60/(40-17), 6.54LPM.
I would expect the rated flowrate of that shower to be ~ 9LPM at a dP of 1.0bar.
It would be interesting if you measured the shower flowrate, outlet temperature and mains temperature when the 1.0bar PRV just starts feathering (lifting), that will give a good idea of the condition of the heating can, scaling etc.
 

Attachments

  • Mira Sport (2007) TCO.jpg
    Mira Sport (2007) TCO.jpg
    367.1 KB · Views: 15
All mains supplied showers also have another protection, a "pressure switch" that when the solenoid valve is energised, the pressure pushes on a a cam or levers to close one or two micro switches to supply power to the heating can element(s), if the mains pressure is too low or fails then the power is switched off to the heating can, some people have to run on one heating element only, at times of low mains pressure, because reducing the flowrate increases the dynamic pressure sufficiently to close the one micro switch to give 1/2 power, far better off installing a integrally pumped electric shower fed from the CWSC if thats the case or, even though it invalidates the warranty, install a PRV (pressure reducing valve) set to 0.5bar and supply the (integrally pumped) shower this way, works quite well if no CWSC installed.
 
Electric showers are designed to give their rated flowrate at a 1.0bar dP so not surprising that the 0.5bar PRV is lifting. All showers also have a dual temperature thermal cut out, TCO, the first (Triton&Mira) stat operates at 48C and self resets, the second, at 75C, does not reset and the TCO must be replaced.

My present mains temp is 17C.
A 10.5kW shower flowrate will have to fall to, 10.5*860/60/(48-17), 4.86, say 5.0LPM before the 48C TCO kills the power to the heating element with that mains temp. At a fairly typical 40C showering temp, the flowrate must be, 10.5*860/60/(40-17), 6.54LPM.
I would expect the rated flowrate of that shower to be ~ 9LPM at a dP of 1.0bar.
It would be interesting if you measured the shower flowrate, outlet temperature and mains temperature when the 1.0bar PRV just starts feathering (lifting), that will give a good idea of the condition of the heating can, scaling etc.


Interesting data John, thanks for filling in the official background to this. I knew there would be temperature cutouts but I was totally unaware of the setup of the system with two - and with only one resettable. That's another reason to get the pressure relief side correct so the temp side doesn't need to activate due to restricted flow.

Your calculation of flow rates is interesting, I hadn't thought of looking into the maths of it. (I'm a maths lover but, if I'm honest, it never occurred to me that you would do that.) I can find Flow Rate = Heat (kW) / 4.2 (Specific Heat of Water) x Temp Rise and work from there but that gives very different answers to you. I guess this is most likely down to differing units. The 60 I assume is hr->min. What does the 860 represent?

I'll try to do a flow rate test and see how that pans out. It is easy with the handheld head but more difficult with the overhear rain shower of course. And maybe it should be performed at the same height as the heater capsule for a more relevant result referenced to the heater unit. Not sure if it would make much practical difference or not.
 
Got it! kilowatt-hours (kWh) -> kilocalories (kcal) per hour? If so that makes sense now. Thanks.
Something like that, 3600/4.2 is (almost) 860, also handy if calculating energy required to heat a vol of water, ie, energy required to heat say 200L water from 15C to 60C, 200*(60-15)/860, 10.47kWh.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Why aren't PRD/PRV devices made resettable?" which is posted in Showers and Wetrooms Advice on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
Bordonbert,
Last reply from
John.g,
Replies
18
Views
1,617
Back
Top