PaulT
Having a bit of a head scratching moment and would appreciate some advice. I've just been called out to a Worcester 28 CDi RSF, the problem is that boiler will not fire when there is a demand for hot water only, however, if the central heating is turned on for approx 10-15 minutes it will fire and provide hot water. It will continue to fire for hot water when a demand is created for about 10-15 minutes after the central heating has been turned off, but once the system cools it refuses to fire for hot water only. I initially thought the diverter valve was faulty (as did the last 3 GSR engineers that had looked at it). I followed the fault finding guide and whilst I was testing for continuity at ST16 (2 x pink wires) the boiler instantly fired for hot water when I connected the terminals. Now thinking there's a problem with the PCB but would appreciate your thoughts as the customer is an elderly lady and I don't want to replace an expensive PCB if you guys think the problem lies elsewhere. I'd really appreciate your opinions.