Hi
about an hour ago all the lights in my house tripped out. I went to the fuseboard and one switch was down. Flicked it back and it tripped out immediately.
few moments later theres and acrid smell and a little smoke in the room
tracked the smell down to the boiler, took the cover off and was met with this (see photo)😳
have got someone coming out tonight to look at it. In the meantime have turned the power off.
Any idea what would cause this earth wire to melt?
It’s a Worcester Bosch junior 28, has been in about 8 years without any problems
Go to the white box adjacent to the boiler, it will have a fuse access panel. Turn the switch off take out the fuse. I may have a red monitor light as well which will go out. You have been very lucky.
centralheatking
centralheatking
cheers, have just done that
When you say ‘very lucky’, I’m guessing we were close to a big bang or fire?
Any idea what would cause this? I’ve had a good look and it’s just that earth wire that’s melted and scorched the plastic casing.
Also, the powers now isolated for the circuit it’s on. Presumably I can keep the gas and water on? (Engineer coming later on)
Tens, if not hundreds of amps flowing as a result of an uninterrupted fault. The boiler should have been protected by small fuse, typically 3 amp, in its mains supply, which would have prevented this. My guess is the boiler was wired into an unfused, or incorrectly fused, junction box.
You're lucky you still have a house and any occupants are alive. Get Bosch to repair the Boiler and a properly qualified electrician to check its supply. (It would be prudent to get them to check the whole house while their at it.)
As Chuck stated if your boiler does not have a white box adjacent with a 3 amp red fuse then your trip has done its job, picked up high demand and saved you. Take this very serously indeed that earth wire has melted due to heat the source of the problem needs tracking down. chking
Thanks all, That’s quite frightening 😳
I’ve taken a look and you can see where the earth wire has melted into the adjacent grey wire (see pic). You can see the scorch marks on the casing too.
no other wires in the boiler seem to be affected
Interesting that the "earth" cable seems to be damaged - unusual to say the least.
Looking at the photo I wonder if the connections to the blue item "connected" to the earth cable and created a dead short - in this case I would have expected the 3A fuse in the boiler supply to fail - was the switch down the MCB or RCD?
I’m thinking the adjacent fuse box has been bypassed. As I turned it off on one of my attempts to get the mains power back on, yet it all tripped out regardless.
[automerge]1578314630[/automerge]
Switch was down on the RCD
sparker so probably the the high voltage wire had a bit of the insulation missing so arc across
As these guys have said there should be a 3 amp fuse on incoming live to boiler system. Like I said though IF you have a bank of MCB's protected by an RCD this will have tripped before the fuse in the event of an imbalance most probably. If your fuse board hasn't got RCD's then the MCB will have tripped do to the ground fault overload
In the case of a dead short, whether the 3A blows, the MCB in the fuseboard or RCD trips is never consistent - sometimes its the RCD and the fuse or MCB...
Often see such faults in back boxes where the box isn't deep enough and the cables are crushed together - then its a matter of time before the sleeving fails ........ then the bang and the black scorch mark
Well done you are ok now, sit back ...cuppa tea and wait for experienced electrician...do let us know what he says as we like feedback it helps us to learn more. centralheatking
To answer your question redd yes fires can be caused from faults like this, however the fuse and MCB should protect the system from this. RCD's protect people from a shock and work by detecting an imbalance between phase and neutral current, ie when theres an earth fault like you've just experienced
yep, leave the breaker off. Burnt out earth wires can be a sign of another fault not related to the boiler.
It would appear that PF can do electrics ....well done all...just goes to show We are the Senior Trade
always knew this anyway did we not ! ? ....centralheatking Is there an Electricians Forum ? yes its under a stone
somewhere but nobody knows where ....chking
Have a degree in electrical engineering and do frequent the other forum, lol
I tend to only look at ops that are either pure gas or electrical, my best friend is plumber 😛
I have a friend who is an Electrician we have had him with us for years...we drink with him
...his name is 'Mad Ian' ..he is quite often 'short on his round' usually never buying me a beer before he slopes off ...but we like and most importantly trust him.......centralheatking
I imagine the ground fault is somewhere inside the boiler somewhere. Lots of places and components where this can happen. I hope this sudden rush of current hasn't damaged any more parts. Might be advisable to have both electrician and engineer there at same time
We’re back in business!
Looks like it was a plug socket in the kitchen (same circuit as boiler) that was at fault. As the electrician took each socket on the circuit out one by one, this one was all burnt out inside. The live wire had melted onto the earth cable. He says the live wire wasn’t secured in the terminal properly and had just come loose over time.
presumably this had made the earth wire ‘live’?
I’ve no idea why it then went into the cellar and nearly set the boiler on fire, when everything else is fine?
Anyway a couple of new sockets later, plus new fuse and socket fitted to boiler supply and all seems well.