Attended this on friday heating and hotwater cut out after about two minutes , slow flash on blue light mainly on.

Reset boiler and same same, replaced flue stat and temp stat but still same fault .
 
Sorry gas pressure and fga all good , checked electrical connections , pump was good and fan was good .
No blockage in condensate or any obstructions in flue.
 
Could the heat exchanger be blocked ?

I’ve added the fault diagram.

83B1F19A-C2A4-4BBE-805A-72FDB5D092BD.png
 
I checked most if that i thought hex could be blocked as when put it in service mode it locked out quick sharp. Mentioned it to customer and she went nuts as boilers only about 6 years old lol,,,,,,oh the joy
 
Get the red/orange burner gasket and an electrode set, remove the burner and check the top baffle. I have come across a few with splits or holes in that give similar symptoms.
 