When our system gets nice and hot the rads fill up with an unidentified gas. I burnt some and it had a clear blue flame, orange edges and left soot on the bleed key and molegrips I was holding the key with. Any ideas? It's a brand new boiler and 15yr old rads. Open vented.
 
hygogen is the gas that is genraly produced is the heating system its the seperation of the water make up wich is a sign that the sytem is'nt prone to air oxygen getting into it and causing rust ie: sludge build up .
so I was led to believe at collage anyway
 
Time to get the system flushed properly. Hydrogen gas is a by product of the corrosion taking place in the syetm. Also get the cold feed/open vent configuration checked as air ingress can accelerate the corrosion problem. All this should have been done when the new boiler was fitted.
 
Sorry for delayed response, I can't find my way round this site very easily! I have tested the ph of the water and it came up neutral. Also, the formation of soot left me confused - I though hydrogen burned clean? Also, I have been told that if it was hydrogen it would burn rapidly (ie pop), while this burns slowly and maintains a flame - I have even managed to video it. My thoughts were methane from some kind of biological action, but it is interesting that none of you proposed this. I see fernox have an anti bacterial cleaning solution - but are such things rare? I would have thought that the power flush that preceded the boiler being fitted would have got rid of nasties, but is is a 10mm microbore system. Still think it's hydrogen? My plumber is offering an air seperator, labour free, parts only cost. Should I accept this fix?
 
Yes mate you could try the air-seperator as that could help it also i believe that getting it power-flushed would not be a bad idea either a bit pricey though! Good luck anyway's!
 
OK, I now know for certain it's hydrogen; I collected some in gas syringe and it went BANG when I lit - took me a bit by suprise! I now need the plumbers' point of view as to what I can reasonably expect my plumber to do. Is it possible to do a decent job at cleaning and protecting the system, and have this problem? If not, should I expect him to repeat the powerflush that was supposed to have been done, or what? The water also has bits of black oxide and what looks like tiny whisps of snot in it. I like my plumber, but he says he has never heard of gas problems such as this in thirty years, so I'm having difficulty in knowing what to do to get him to understand. Should I have to pay again to get this sorted? I don't feel like I should! The fact the cold feed tank is full of sludge suggest of a lack of attention to detail when it came to cleaning out - wouldn't you wash that out?
 
Its difficullt to judge how another engineer has done without knowing the full details and what sort of condition the system was in before he started.
In answer to your question. Yes in theory a powerflush can completly get rid of this problem but it does and can take a long time.

How long did the engineer take and how much did he charge?
 
I had a Worcester boiler fitted and was told that the system had to be cleaned to the manufacturers requirements for the guarantee to be valid. I was told that this would include a powerflush. I pointed out at the time that it was 10mm microbore but this wasn't reqarded as a problem. I requested one rad removed and cleaned out because it had a large coldspot low down, and this was done with some success. I don't know how long they took because I wasn't in (whole job took 2 days) and the bill wasn't itemised. The job was as follows:

Installation:
  1. Remove existing boiler, make good flue hole
  2. Fit new hot water cylinder stat (lower position)
  3. Install new boiler in downstairs WC, on wc wall with flue going to the right
  4. Run condense to WC soil pipe
  5. Run flow and return to new boiler making sure they are correct
  6. Electrics to boiler
  7. Install new 7 day programmer
  8. Power flush heating system to manufacturers instructions
  9. Fit 2 x pump isolating valves
  10. Commission and test to current standards
  11. Disposal of rubbish
Total £2,325.00 inc. VAT


PS the boiler is an 18ri, the cleaner was Gold 300, and inhibitor is Gold 100. We bought the house last year, and it is approx 15 years old. Don't know how well maintained the system was, but works fine now except for bleeding bubbles!
 
Last edited by a moderator:
I ordered some of that gold 100 from a company cold calling me selling it at about £5 a bottle, compared to fernox, sentinel etc it's like a bottle of water I think they are rip offs and their cleaner would probably struggle to clean a new system. Id go get some sentinel x700, pour it in you heating tank before bleeding your rads again and get the system hot for a while then ask your plumber just to come round and drain down and put some proper inhibitor in like sentinel x100 or fernox f1

If that doesn't work it will need power flushing but make sure he uses proper chemicals
 
Last edited by a moderator:
i agree over the chemicals, it's always best to use chemicals from a well known manufacturer like fernox or sentinel. although having said that i have no nonsense in my van at the moment which has a bottle identical to the fernox one, who knows could be made by the same company?
 
all chemicals now have to be build cert approved to prove there up to the job in hand,however some one on here posted up the results of the build cert findings the strength/concentration results are interesting
 
I am assuming from your responses that as a minimum the system needs a refill with a decent inhibitor. My problem is that my plumber instead wants to fit an air separator (which I assume would happily remove the bubbles, while my radiators continue to corrode away in the meantime?) How do you advise I proceed - after all, I can't meddle in his decisions without the danger of taking responsibility away from him to fix it. On the other hand, if an air separator is fitted, the noticeable symptoms may go away and he can walk away while my rads rot. What do I do now? PS thanks very much for all your help - I am feeling a lot happier now!
 
allow him to proceed with the air seperator, but ask him to add a decent cleaner and return at a later date to drain down and refill with a decent inhibitor.
you would not be asking him to do something that is contradicting his intended course of action, simply providing ongoing protection for your heating system.
 
just insist he uses fernox or sentinel that way you will be sure a decent make was used, ok it will cost more but for peace of mind in the long run you can't go wrong really.
 
If so, have you got a link to show a good general arrangement? He mentioned that the pump would be moved to the vertical and would be pumping down. I know that the pump is just circulating the flow, but I though pumping down hill was just bad practice to be avoided generally? (I bet you plumbers wished the internet had never been invented! What do the say about a little knowledge...)
 
Last edited by a moderator:
You could ask him to put some calchem 3 in1 in the system while he's fitting the air separator. This stays in permanently and doesn't need flushing out, have had some really good results shifting cold spots with this.
 
How often are the rad's filling up with air? If its regularly its drawing air in so either its piped wrong or the pumps set to high for the configuration. It may also explain why it burnt for longer if there is a considerable amount of oxygen in there aswell rather than just a build up of hydrogen.
Air seperaters from my experience, are normally used if you have a low head installs, they shouldn't be required if you have 600mm plus between water level in tank and top of system. Did he fit a new pump?
 
I think the MI specificies a mains flush and does not mandate a power flush...
 
john it might be worth finding out what the dosage rate was with the inhibitor used ( gold 100 )
there is a limit to the amount of radiators 1 ltr will treat if your system is a large one or many rads then maybe it needs moore inhibitor introducing to the system , perhaps a call to fernox or sentinel or preferably the gold the company used im sure they will have some answers . let us know if you get anywhaere with it , Smiley
 
hi John is there a differential by-pass fitted? is it possible that an old sledged up micro bore system is not allowing enough flow through the boiler now that its got a new pump? causing it to pump over into the exp. tank. this would allow fresh oxygenated air to enter the system
make sure that the feed and exp. pipework is correctly configured if u used the old pipework the f & e maybe connected across the flow and return, the new boiler may require a close coupled connection using either the flow or return (cant remember which)you said the pump had been moved could be the feed is now on the wrong side
I would get up in the loft and have a look what's going on in the tank
fitting an air ejector will treat the symptoms but wont tell you the cause good luck
 
Feed tank is in the loft, well in excess of 60mm above system. If I bleed all the radiators it all goes nice and quiet. Starts making the popping noises normally next day. The noise is loudest as the thermostatic heads start to close once the house has heated up in the morning. After a couple of days there is enough gas to create glugging noises. I have tried the pump on its highest setting, and it doesn't seem to create any problems. I have even tried holding a pint glass of water over the vent while my wife switched the system on (a tip i read on the web) - no more that a slight dip in water level - hardly conclusive I know but the pump doesn't seem to be the problem. In fact I can run the system cool for a few days with no problems even with the pump set quite high, it only seem to be when the water gets really hot that the the gas occurs - totally wierd, but in my simple GCSE science mind I imagine the corrosion reaction occurs more quickly at higher temperature. Maybe enough hydrogen bubbles create elasticity in the system which then draws air through the vent as the water can 'slosh' more - how's that for a long shot! PS he didn't fit a new pump.
 
Can you take a picture of your controls etc, are you getting any water out of your overflow from your F&E tank particularly when the system is at its hottest??
 
There is only and on/off switch and a thermostat setting on the front, I was told to leave it at 3/4, but to turn it up in cold weather. I have left it on 3/4.The water level does go up and down in the F&E tank, but never empties and never overflows, although I will check again.
 
hi, microbore central heating system are much harder to power flush as the pipework is much smaller, the powerflush works on the basis of flow and with small bore piping you cant always get the flow through the pipes, you may need to change the piping or change some of the rads, or maybe try a stronger chemical to flush the system poss fx2,
hope this helps

www.shawsplumbingandheating.co.uk
 
Hi, microbore piping is much harder to powerflush as the pipe are much smaller, powerflushing works on the basis of flow and with small bore pipes you cant get the flow through the pipes, you may need to replace the pipework or change the rads or try using a stronger chemical to powerflush the system poss fx2 and the header tank should always be removed and cleaned out otherwise the dirt will just re- enter the system, hope this is helpful.
www.shawsplumbingandheating.co.uk
 
John is there any plastic pipework showing on the system do all the rads have TRV's ( thermostatic rad valves ) fitted if so as asked earlyer on by some one has it got a bye pass valve fitted anywhere

if there is plastic pipe how old is it, and is it a barrier pipe ? because none barrier pipe causes oxygen to be obsorbed into the systems water wich i have known to kill a new boiler withing couple years easily . the bye pass is requierd due to TRV's all shutting down as being upto temp this may cause pumping over to happen.
other than that how old are the rad valves maybe one or more could be sucking air in if they are in a negative presure area of the pump . just a few thoughts
plus what colure is the water within the system clear / black / brown etc ?
 
The pump is not a new one, but even so the plumber did double check the configuration, and did mention about the possibility of pumping over so I assume he checked for that. I'm glad you mentioned about treating the symptoms coz that's what I'm worried about too!
 
No plastic pipe, and all TRV's except one in the hallway, and there is a bypass with a gate valve on it. The plumber has looked at this, and recommended that I upgrade from a 3 way to 2 x 3 way valves with an automatic bypass. But it used to be fine! The rad valves are 15 years old, I am guessing. However, since the pump is a few centimeters upstream of the cold feed I am assuming this is the only area that could possibly 'suck' in air? I must admit, it is one particular TRV upstairs that makes a lot of noise, and the same rad that gets most gas - but no negative pressure surely? - the F&E tank is in the loft. PS the water is clear with black flecks and occasional translucent 'floaty' bits!
 
Last edited by a moderator:
Status
Not open for further replies.

Reply to Gas in rads in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
272
PSxxxxxx
P
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no...
Replies
6
Views
249
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
542
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
206
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
428
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock