The copper gas pipe to my boiler in the loft runs between joists and sits on the plasterboard. I understand that it should not be covered by insulation. Why? Is it satisfactory to create a dome over the pipe with upside down guttering and then put fibreglass insulation over the top please?
 
Think your getting confused with wires ideally you don’t want wires/ cables encapsulated in insulation as it de rates there load capacity

The gas pipe should have its own clips / supports but other than that never heard of no insulation around it
 
Think your getting confused with wires ideally you don’t want wires/ cables encapsulated in insulation as it de rates there load capacity

The gas pipe should have its own clips / supports but other than that never heard of no insulation around it
Thanks Shaun
I'm basing this on BS 6891:2015 on low pressure gas pipework which says 8.9.13 Pipework shall not be laid below or within roof space insulation material.
 
Is it staying non habitable/ no floor going on it ?
 
I'm not sure this is the reason, so treat it as a guess, but if some types of insulation get wet (die to condensation / leaks in the roof space) it creates a corrosive environment that attacks pipes. I've only seen this with steel pipes, but copper corrodes nicely too.
 
Lagg it with pipe insulation doesn’t touch any insulation then tbh seen most bungalows with new insulation over the top of pipes with no problem
 

Reply to Gas pipe under loft insulation. in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

I have decided to remove the timber floor boards and joists as they are effected by damp and rotting. Was hoping to infill and have slab and...
Replies
2
Views
348
[ASIDE: I did wonder if this was the best forum for this but figured as it was a boiler related issue that the gas engineers would be dealing...
Replies
5
Views
269
Hi all, this is probably a daft question but I need to run my cold feed from one side of my wall mounted boiler to the other. Running it beneath...
Replies
2
Views
219
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16...
Replies
0
Views
237
Bungalow built in 2001. All copper pipework (water and heating) runs in channels of expanded foam polystyrene between a concrete floor and OSB...
Replies
8
Views
333

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock