So, does this indicate to you so far, that the behaviour is the same as with the HW enabled, ie that the system will still "never" need top up no matter how much air is vented?. If this is the case, then that would indicate that you are pulling air into the system and not venting residual air. If the PHE was causing the problem then you would expect the overall boiler pressure to gradually decay? now that its (the PHE) out of the picture.

Yes, that’s my understanding. I haven’t topped the system up since…I don’t know when!

Is it safe to assume that we’re pulling in air BELOW the towel rail?

I can fairly easily cap off the top floor. And run the system and see if that stops air coming in.

I can cap off the middle floor, just leaving the ground floor, too - but obviously trickier as it’s winter and house will be cold.

Any other suggestions welcome!
 
I honestly don't know or even see how air can be getting in anywhere from outside, gases being generated inside the system would explain it but your hydrogen test was negative.

What about just shutting both isolation valves on that towel rail for a few days and see does air appear somewhere else?.
 
I honestly don't know or even see how air can be getting in anywhere from outside, gases being generated inside the system would explain it but your hydrogen test was negative.

What about just shutting both isolation valves on that towel rail for a few days and see does air appear somewhere else?.

I'll shut the towel rail off later in the week when the kids are away.

I fitted an automatic air vent from Aladdin on the towel rail. The last one didn't seem to work but this one definitely released air when I opened the valves on the towel rail again.

Just a few odd things I noticed when fitting it...

When closing the valves on the towel rail and opening the bleed valve, there was air for a few seconds and then water/air mix for a few seconds.

Hard to see but the water level was about an inch (why have I suddenly gone imperial!) below the top of the towel rail:

1635268980648.png


About this level:

1635269043404.png

And this is the muck inside the towel rail:

1635269012805.png


Is this considered dirty?
 
The dirty water is a result of air ingress somewhere. The free oxygen is reacting with the iron content in radiators and causing corrosion, the result sludge build up. I know John disagrees with me but I'm still not convinced you don't have part of the system under negative pressure and drawing in air. The black iron oxide (sludge) is proving that.
 
The dirty water is a result of air ingress somewhere. The free oxygen is reacting with the iron content in radiators and causing corrosion, the result sludge build up. I know John disagrees with me but I'm still not convinced you don't have part of the system under negative pressure and drawing in air. The black iron oxide (sludge) is proving that.

Ok. So how do I diagnose this further?

Is it a matter of replacing pipe work?
 
I am pretty much convinced your problem is a pressure problem. Somewhere in the system under negative pressure is a weak point drawing in air, why it only accumulates in that one particular towl rail I can't answer. If the layout of the boiler John shared some time ago is correct then at least some of the system is under a negative pressure. If there's a weak point on this side that is below atmospheric pressure while the pump is running it will pull in air. Pressure is always trying to reach an equalibrium. I personally don't think how the boiler pipework and vessel location is laid out is correct but there must be somewhere with a weak joint, almost certainly on the suction side of the pump.
 
I am pretty much convinced your problem is a pressure problem. Somewhere in the system under negative pressure is a weak point drawing in air, why it only accumulates in that one particular towl rail I can't answer. If the layout of the boiler John shared some time ago is correct then at least some of the system is under a negative pressure. If there's a weak point on this side that is below atmospheric pressure while the pump is running it will pull in air. Pressure is always trying to reach an equalibrium. I personally don't think how the boiler pipework and vessel location is laid out is correct but there must be somewhere with a weak joint, almost certainly on the suction side of the pump.

By suction side do you mean the return side?

The pump is going, that’s positive?

The return is under negative?

I guess what I need is a method of how to isolate the problematic area. Is it likely to be a rad? A joint under the floor?
 
Suction side is the inlet to pump. The discharge side (after the pump) should be under positive pressure, relative to pump ∆P (delta P).

If during summer use you accumulated no air then that would suggest as you say something somewhere is weak. You could go around tightening all connections above the floors, if the problem lies beneath floors that's a bit more of a problem.
 
Suction side is the inlet to pump. The discharge side (after the pump) should be under positive pressure, relative to pump ∆P (delta P).

If during summer use you accumulated no air then that would suggest as you say something somewhere is weak. You could go around tightening all connections above the floors, if the problem lies beneath floors that's a bit more of a problem.
Really hard to say, there was a tiny bit of air over the summer (a tiny spurt and then water) but not this much. I’m bleeding every day for between 3 and 10 secs.

I did notice this on one of the rads:

BEB6BC04-19D3-40F0-9D91-C55A0B9E9251.jpeg
This rad is very rarely on as the room gets warm during the day and is cool at night.

Could this be a cause?
 
Would definitely prefer to see the EV installed on the pump suction side like this Vokera Combi but there must be thousands of Baxis with them on the discharge side.

1635283157673.png
 
That rad lockshield looks like it's been bombarded with PTFE on the return, possibly because of a leak on the old system under positive pressure and could quite well be the culprit. I would consider remaking that joint. Where is that rad in relation to the towl rail?
 
That rad lockshield looks like it's been bombarded with PTFE on the return, possibly because of a leak on the old system under positive pressure and could quite well be the culprit. I would consider remaking that joint. Where is that rad in relation to the towl rail?

This is on the same floor, about 8m away.

What would you recommend when redoing the joint? How many winds of PTFE?

As this rad is almost always off I could always just cap off the pipe work for a few days and see if that resolves?

I’m not adverse to doing this myself but I must admit I don’t like it. I fit an 8000 BTU rad in the kitchen and hated every minute of it!
 
Ok. Close both valves for a day or two and see if it draws in air. I'm willing to bet based on the state of that lockshield and the crude attempts to fix an obvious problem that no air will be drawn in to the towel rail. If this proves correct you would need to remake that joint. You shouldn't need any PTFE or jointing compound on a valve if holding true.
 
With EV on the pump discharge, the way I see it is that the pressure at any point in the system will be reduced by the pump head so presumably a severe restriction can allow air ingress at a weak point(s).
 
Ok. Close both valves for a day or two and see if it draws in air. I'm willing to bet based on the state of that lockshield and the crude attempts to fix an obvious problem that no air will be drawn in to the towel rail. If this proves correct you would need to remake that joint. You shouldn't need any PTFE or jointing compound on a valve if holding true.

ok, will try.

here is my attempt at fitting the rad in the kitchen.

8DD1AA5F-BFBC-4CA0-A038-14404DF883F7.jpeg
there is some blue staining underneath the TRV bit and also on the pipe coming out the wall. The thing is, when the floor is mopped this pipe can get wet. That would cause the blue staining?

I put loads of PTFE on this rad because the lad that fit two other rads in the house for about £300 said you need 25 turns of PTFE on these acova rads?
 
The rads closest to the boiler and at lower points in the system should be under positive pressure and a weak point would be recognised as a drip. Any points higher in the system and weak could well be under negative pressure.
 
The rads closest to the boiler and at lower points in the system should be under positive pressure and a weak point would be recognised as a drip. Any points higher in the system and weak could well be under negative pressure.

OK. That is useful.

Any rad above the ground floor could be a culprit.

The towel rad also has an electric heating element that (I believe) only has a rubber seal on. There’s a T piece where the CH system connects in.

I guess I can go around switching off each rad for a day or two. If the air stops, I know it’s the rad that is off.
 
The rads closest to the boiler and at lower points in the system should be under positive pressure and a weak point would be recognised as a drip. Any points higher in the system and weak could well be under negative pressure.

Just thinking about this…

Any other rad in the house spits out water instantly. This means they’re under positive pressure (water being forced out).

If the rads on the second and third floor were under negative pressure I’m guessing opening a bleed valve would cause air to be sucked in?

If so, this ain’t the case. When I open them to bleed there is only water coming out.
 
That depends. If you're bleeding the rads with the boiler and pump off then you will get water come out. If bleeding with them on then you should draw air in if under negative pressure.
 
That depends. If you're bleeding the rads with the boiler and pump off then you will get water come out. If bleeding with them on then you should draw air in if under negative pressure.

Ok. So if the heating is on I can test if there’s negative pressure if any of the rads. I can do this as well.

I’m just keen on verifying the problem before I start replacing pipe work!
 
My thinking on this, especially in view of the above ongoing air ingress is that negative pressure is NOT required, and that with any slight leak, even a weep, that air finds it far easier to gain access than for the water to seep out?. Maybe not quite alalogous to oxygen gaining access through "solid" plastic (non barrier) piping, who would have believed that but it does happen.

There was a good post on here a few years ago from someone (plumber) who had experience of two houses, one sealed, the other OV, where both had lengths of non barrier piping, the sealed one kept getting air problems but the OV one didn't, he put this down to the fact that the OV one could constantly vent any air continuously through its 22mm vent.
I think I may have a few lengths of non barrier piping in my loft area which has two rads but again never ever get air problems probably because of the OV system?.

Actually, both these rads run with a very very slight negative pressure at the vents but because the whole system is drop tight ( I installed it !) then no problems.
 
Last edited:
My thinking on this, especially in view of the above ongoing air ingress is that negative pressure is NOT required, and that with any slight leak, even a weep, that air finds it far easier to gain access than for the water to seep out?. Maybe not quite alalogous to oxygen gaining access through "solid" plastic (non barrier) piping, who would have believed that but it does happen.

There was a good post on here a few years ago from someone (plumber) who had experience of two houses, one sealed, the other OV, where both had lengths of non barrier piping, the sealed one kept getting air problems but the OV one didn't, he put this down to the fact that the OV one could constantly vent any air continuously through its 22mm vent.
I think I may have a few lengths of non barrier piping in my loft area which has two rads but again never ever get air problems probably because of the OV system?.

So this means the problem could be anywhere, right?

I’ll do what I can do find the problem but short of ripping out pipe work on 3 floors I may never find it.

If the auto air vents work on the towel rail, is this equivalent to an OV system? At least air makes it’s way out of the system?
 
Yes, I think it could be, but if you fix the obvious ones and give the system a thorough cleaning then would think that you will be OK.
I wouldn't compare auto vents with a OV as the auto vent tends to operate more on/off and I certainly wouldn't dream of using them as a cure by installing them on all rads, maybe OK on your towel rad as a temporary measure, remember there was a magic Aladdin lamp but not ditto for Aladdin's auto air vents.
 
Can I just say that you have mentioned replacing lots of pipework at least twice and I have never agreed with you, I am not suggesting that. If air is being drawn in then it will be coming from a weak fitting somewhere
 
Can I just say that you have mentioned replacing lots of pipework at least twice and I have never agreed with you, I am not suggesting that. If air is being drawn in then it will be coming from a weak fitting somewhere

ok, so in your opinion it’s a weak fitting. That’s a relief somewhat!

I guess I’m going to “worst case“ scenario which is lift up floorboards and smash out a couple walls!

I may try and find a local heating engineer to do this. I’ve struggled in the past to find anyone reputable.
 
@SJB060685 haven’t had much luck getting an engineer along.

Spoke to a bloke this afternoon who said I’ve either got a leak or the cold water supply is somehow feeding into the system. I said I removed the filling loop and he suggested that the cold water supply is somehow piped into the heating. I don’t see how this is possible!

I need to isolate a couple rads this week to see if they are the source of the problem.
 
Presume there was no noise before with DHW on?. Can you shut down the boiler and just open the same "hot" tap the same amount and see if noise is gone, this may at least prove that the noise is from the primary side.
 
Shut off both CH & HW (or switch off the boiler completely) and open the hot tap, this will just run cold water (now) through the combi and see if noise is gone.
 
Shut off both CH & HW (or switch off the boiler completely) and open the hot tap, this will just run cold water (now) through the combi and see if noise is gone.

@John.g sorry for the delay.

I ran the hot water with everything on. There was the whistling noise.

While the water was running, I switched the boiler off entirely. The whistling sound was still there.

What does this mean?
 
If you were still running the cold water through the combi (hot water tap open) tht em the whistling is caused by this and not the primary water (dirty water).
So don't really know what it means in the context of air in your rads etc.

Can't post on my Windows10 laptop for some reason or other.
 
If you were still running the cold water through the combi (hot water tap open) tht em the whistling is caused by this and not the primary water (dirty water).
So don't really know what it means in the context of air in your rads etc.

Can't post on my Windows10 laptop for some reason or other.

If you were still running the cold water through the combi (hot water tap open) tht em the whistling is caused by this and not the primary water (dirty water).
So don't really know what it means in the context of air in your rads etc.

Can't post on my Windows10 laptop for some reason or other.

Have you blanked off that leaking non return valve.

Also just to be sure (again) did you say that with the boiler (&circ pump) ON that you are getting water out of all the rad vents apart from towel rail which emits air initially, does the towel rail also emit water eventually with the boiler/circ pump on?.
 
Have you blanked off that leaking non return valve.

Also just to be sure (again) did you say that with the boiler (&circ pump) ON that you are getting water out of all the rad vents apart from towel rail which emits air initially, does the towel rail also emit water eventually with the boiler/circ pump on?.

@John.g I got a new filling loop and attached one of the isolation switches like this:

IMG_9070.jpg


When I removed the old filling loop it still had some water in despite not being used for weeks (if not months).

I then switched on the CH system and went round all 9 rads in the house.

Every rad bled water apart from two. The rad in my son's room bled a little air, then water. The towel rail in the bathroom bled quite a bit of air (as usual) and then bled water.
 
Can shut off that towel rad "permanently" for a few days and see does the air appear somewhere else and if noise subsides?.

I can but we had the same problem before this towel rail was installed. The air just appeared in one of the top floor rads.

I haven’t heard the gurgling for a while now. Just air.
 
Can shut off that towel rad "permanently" for a few days and see does the air appear somewhere else and if noise subsides?.

@John.g I isolated the towel rail for 3 days. Switched on the electric element.

On day 1 there was a tiny bit of air in the rad in my sons room. No air in any other rad.

On day 2 and day 3 there was no air in any rad.

On day 3 I checked the towel rail. There was a bit of air in there but not loads.

I opened up the rad valves last night. I checked this morning and there was a bit of air in it again.

So I’m thinking there’s two possibilities:

1. The towel rad valves are cheap/somehow letting in air? This needs refitting.

2. The pipe work before the towel rad is filling up with air.

Which is more likely? With the rad shut off, if there was air getting in elsewhere in the system, would you expect the air to end up in another rad?
 
Wouldn't be surprised at a bit of air in towel rad with element on.
Would suggest repeating test.
isolate the towel rail with the electric element off and the bodge rad off for a few days.
if no air, open up the bodge rad and if still no air after a few more days reopen the towel rail. If you then get air its the towel rail that's the culprit.
 
Wouldn't be surprised at a bit of air in towel rad with element on.
Would suggest repeating test.
isolate the towel rail with the electric element off and the bodge rad off for a few days.
if no air, open up the bodge rad and if still no air after a few more days reopen the towel rail. If you then get air its the towel rail that's the culprit.

Ok, just so I’m clear…

Isolate rad via valves. Leave heating element off. Leave rad for a few days.

After a few days, check if there’s air in the rad.

After a few more days, reconnect rad via valves. If there’s air then the radiator is causing air?
 
OK, maybe slightly different method but either way you want to establish if either or both the towel rail &/or the sons rad are the cause of the air.
Shut towel rail isolating valves off both sides then open air vent to ensure valves are tight and not passing. Leave or shut off the electric heating element. After a few days if no air anywhere then towel rail is the culprit, If still getting air shut off the sons rad both sides, if still getting air then problem probebly caused by weeping pipes?
 
OK, maybe slightly different method but either way you want to establish if either or both the towel rail &/or the sons rad are the cause of the air.
Shut towel rail isolating valves off both sides then open air vent to ensure valves are tight and not passing. Leave or shut off the electric heating element. After a few days if no air anywhere then towel rail is the culprit, If still getting air shut off the sons rad both sides, if still getting air then problem probebly caused by weeping pipes?

Ok, I’ve just switched off the isolating valves on the rad. I bled the radiator for quite a while and there was a lot of water then air then water then air. It took a few mins for that to finally loose pressure entirely.

I took the bleed valve off entirely and topped up the rad with 300ml of cold water.

I then opened the isolation valve for a split second to re pressurise the rad. I bled it again for a few seconds. I think this means the rad is now (in theory) without air!

Are you suggesting leaving the air vent entirely open?

I don’t know what you mean by “sons” rad?
 
If you mean the Towel Rail (your description) rad then yes leave the air vent open. and test system again for a few days.

"I also completely turned off rad in the other bedroom after someone said the joint looked like a bodge job." thought this was your son's rad, if you are still getting air somewhere with the suggested test then isolate this rad as well and test for another few days, ie with both towel rail rad and the bodge rad isolated.

I'm not sure if water still seeps from the pipes with the bodge rad isolated? but if so and if you are still getting air after the second test then this possibly the reason?.
 
If you mean the Towel Rail (your description) rad then yes leave the air vent open. and test system again for a few days.

"I also completely turned off rad in the other bedroom after someone said the joint looked like a bodge job." thought this was your son's rad, if you are still getting air somewhere with the suggested test then isolate this rad as well and test for another few days, ie with both towel rail rad and the bodge rad isolated.

I'm not sure if water still seeps from the pipes with the bodge rad isolated? but if so and if you are still getting air after the second test then this possibly the reason?.

The “bodge” rad has been isolated for over a week. I haven’t looked at as the room is fairly warm.

The radiator in my sons room is connected and heating fine.

I’ve opened the air vent on the towel rail.
 
@John.g The bathroom towel rail has been isolated for a week.

Before turning on the bathroom towel rail, I bled all the rads today for between 1-2 mins to be sure that there was no air.

Only one rad had a little bit of air in. On the same floor as the towel rail. It wasn't just straight air but a mix of air/water. Maybe 25seconds worth, didn't seem to be that much air. Certainly a hell of a lot less than we had in the towel rail. All other rads were fine. For reference I have 9 rads in the house.

I've put some inhibitor in the system and opened the towel rail.

I'll give it a few days and check the towel rail? If there's air in the towel rail then it's somehow pulling in air?
 
Looks like that but really you shouldn't be getting any air anywhere now IF that is/was the problem, did you or someone say that air might be getting in where the electric heating element is screwed into it?, you might be able to rejoint that.
 

Reply to Gurgling and air in central heating in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

When I turn on our CH there's a lot of noise from one specific part of the system - the pipes on the landing, and one radiator. It sounds like...
Replies
35
Views
2K
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
310
PSxxxxxx
P
Boiler is making a gurgling sound and keeps short cycling. I believe there is air in the the system and I've already bled all the radiators. This...
Replies
4
Views
1K
I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and...
Replies
2
Views
514
losing pressure
L
I need to extend my central heating from my newly built extension in to the old part of my house. I need to feed 3 rads in separate bedrooms on...
Replies
2
Views
174
Back
Top