Evening gents

I have a Worcester green star ri controlled by a Honeywell st9420c controller and wireless thermostat

All working fine this morning now when home from work I’m getting no heating. The light is on on the controller and the digital thermostat is showing the fire symbol but there’s no heating working at all

Hot water is heating up apparently fine and the boiler will periodically fire up and then stop again about 10 seconds later

Any ideas? Had a new grundfos pump and switch fitted 18 months ago

Thanks a lot in advance
 
Do you have a hot water cylinder and zone valves as below ? It may be a faulty head on the heating valve it may be possible to lock the head open its a common fault the motor may be burnt out or the linkage worn so not triggering the micro switch when it moved over . Kop
 

Reply to Help needed on central heating problem in the Canada area at PlumbersForums.net

Similar plumbing topics

Hi, I have a Vailant EcoTec Boiler with a Megaflo. These are controlled by a Honeywell controller. I have one 3 port diverter, where one of the...
Replies
5
Views
294
Hi, I drained the the central heating, to remove a radiator. After refilling it, the heating now won’t work. It’s a combi . I’m getting this symbol
Replies
2
Views
480
I have a home with an oil boiler in a garage turned into a flat, heating both flat and main house, running c plan with two pumps, two motorised...
Replies
0
Views
423
  • Sticky
I thought I'd create a master thread to move all of these similar threads into, over time like. If your central heating doesn't work boiler...
Replies
8
Views
1K
  • Question
Have a sytem boiler with unvented cylinder with 2 heating zones plus hot water in a house we moved into recently. To start with we were always...
Replies
8
Views
469
Back
Top