Discuss Mains feed and vent pipe on vented system in the USA Plumbers Advice area at PlumbersForums.net

Matt0029

Gas Engineer
Messages
1,138
I have a boiler to swap on a vented system. The open vent was presently attached straight to the boiler. And the cold feed is tee'd in to the hot water return near the coil. When I install the new boiler (it's staying vented). Would I be best off changing the cold fill postion I will obviously need to alter the open vent as it did originally tee straight off the boiler.
 
With a view to possibly changing it to what it states in the new boiler manufactors instructions.
 

Attachments

  • Screenshot_20210206_152530_com.google.android.apps.docs.jpg
    Screenshot_20210206_152530_com.google.android.apps.docs.jpg
    285.6 KB · Views: 19
Sounds like it was gravity hot water

and yep either need to adjust one or convert to sealed
 
It’s prob been semi converted
 
Thanks so if I keep vented I should really change the cold feed postion? I need to change the vent anyway. Can I ask the reason for the inverted cold? Is it to stop water pumping back in to the head tank? Thanks
 
Anti gravity loop, stops gravity flow back upto the tank
 
Been looking through some of my old level 3 books. That shows the cold feed to the system tee'd in to the primary return on a gravity hot water system same. Was this done to try and make the primarys circulate more?
 