Discuss Pressure testing 63mm gas pipe in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Depends on spec of pipe
 
Ask what the supply pressure is eg before reg
 
I see in this table it is below 100mb so MOP x 2.5

Screenshot_20181218-230626_Chrome.jpg
 
You need to find out the Mains pressure before the Governor that controls your installation pressure. Cadent will tell you what the supply pressure is in that area. If you get that, I can look in IGE/UP/1 and tell you the pressure you need.
 
Which ever is greater so mop might be 21mbar so 52mbar test

But mip could be 75 mbar so 82 mbar test

So mip is your testing pressure
 
I have talked to 4 people now and they don't know any figures just that the pressure in the mains gas pipe in the road is low pressure. Very frustrating

;D welcome to the world of trying to get info out of the networks
 
Must be a nightmare.

To be honest, Cadent would of had it but it is not there area. It is SGN.

I have found this info though...

Going from that info it is what you have suggested and 75mb for low

Screenshot_20181219-093110_Chrome.jpg
 
G/u65 meter defo commercial
 
Board left of solenoid
 
There you go mip 75 mbar

Mop 23

So test would be 82.3 so 83mbar so you could test the mdpe at 100 mbar
 
There you go mip 75 mbar

Mop 23

So test would be 82.3 so 83mbar so you could test the mdpe at 100 mbar


Thanks for the calculations. As I don't have a gauge that does 100mb, I could do this as you suggested in the 1st place to 1 bar as it is only a soundness test after all. But, as you say it is commercial so should I avoid.

Well if one thing that comes out of this I have learnt a bit about cost of fittings for this size pipe and strength testing.

Thank you all
 
Upto you as it's not connected you could say your only testing the pipe for defective not carrying gas
 
Don't have one

Got a dial gauge eg pressure and an anton 140
 
Bes do a 100 mbar gauge

IMG_3950.JPG
 
So went to pressure test this job but the pipe was not installed to regs. They had run yellow mdpe into the building which if I remember correctly is a no.

I do know the gas board do this though when replacing the mains to the meter inside the house with mdpe by pushing it up the old pipe.
 
So went to pressure test this job but the pipe was not installed to regs. They had run yellow mdpe into the building which if I remember correctly is a no.

I do know the gas board do this though when replacing the mains to the meter inside the house with mdpe by pushing it up the old pipe.
Any pics?
 
into the building is ok under the building no no
 

Reply to Pressure testing 63mm gas pipe in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have done pressure test for 2" high pressure pipe line by closing the pipe with rubber plugs at the ends. It was 3 bar and I kept it for 24...
Replies
6
Views
343
I've air tested pipework for years, typically 4 bar for 30 minutes. I've never had an issue with any pipework that has passed that test...
Replies
8
Views
528
Hi, Non-professional / knowledgeable person here. I'm a Brit in Romania who volunteers for a charity building an old peoples home for needy old...
Replies
3
Views
423
I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and...
Replies
2
Views
519
losing pressure
L
British Gas servicing the above boiler ramped up the boiler to maximum in the installer menu to do flue gas analysis. They also measured the...
Replies
4
Views
604