Hi, I have recently had a water board inspection
This is what the report said about the filling loop on our press unit for a biomass boiler….

There is quickfill pipework directly between the mains water supply and heating supply. This type of temporary connection is permitted under the water supply regulations however the following must be incorporated:
1. Double check valve are required on both upstream (mains side) and downstream (heating side) of the braided temperate hose 2. Remove flexible braided hose when not in Use

I understand you need a double check valve and removing the braided hose when not in use, but why 2 check valves?
 
How many kw is the biomass ?
 

Information on fluid categories if it helps.

Probably gone for the 2 x double check to protect the mains supply and risk of backflow as much as possible without slapping you with an RPZ install notice as you could technically just connect to the downstream side from another source if it didn't have the backflow protection on that as well.
 
The same could be said for a dcv failing tho
True, there is always the risk with CAT 3, but if the water undertaker has instructed it to be installed as long as you've followed instructions you are covered.

Even CAT 4 RPZs fail and as long as they are repaired/replaced within the undertakers guidance time period you are covered. Only true backflow protection is CAT 5 to be honest.
 
True, there is always the risk with CAT 3, but if the water undertaker has instructed it to be installed as long as you've followed instructions you are covered.

Even CAT 4 RPZs fail and as long as they are repaired/replaced within the undertakers guidance time period you are covered. Only true backflow protection is CAT 5 to be honest.

Another down side to rpz is the servicing
 

Reply to Why 2 double check valves on filling loop in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

I’ve noticed on my old Bosch boiler the DCV on the filling loop is fitted to the boiler side of the water supply. And there is no isolator valve...
Replies
4
Views
792
On my Valliant eco tec boiler the pressure guage is on red when cold . I drain a radiator to correct to pressure and it works fine and stays in...
Replies
5
Views
540
Oliver1234
O
Hello, and thanks for taking the time to read. I'm trying to work out if the idea I have is practical? The water pressure in my newly renovated...
Replies
3
Views
420
Hi guys. A couple of things. 1 am I better fabricating bends in 14 mm copper for my ch or are 90 degree elbows fine, ref flow, friction ect. 2...
Replies
0
Views
309
Hello, I live in a two floor semi with a gravity fed conventional gas fired boiler (Potterton Kingfisher MF). The boiler is fed cold water from...
Replies
0
Views
516
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock