If you have changed the head on the valve and you still have the same issue and the centre spindle on the body is moving freely, then it might not be the valve.
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
If you have changed the head on the valve ........
Presumably you have a timer or programmer that turns both the HW & CH on & off. This would be in series with their respective thermostats. All need to function to make the valve work as intended.Timer? Sorry youve lost me...
I’m now confused. Apolgies in advance if I sound rude. So you have changed nothing and still have them same issue?
With what you’ve said I’d be suspicious of the head. Probably best just to replace whole valve like others have said.
Hasn’t this been mentioned already?OK. Thanks, I see your logic.
Hasn’t this been mentioned already?
The motor is designed to be permanently stalled. The motor is fed through resistors & a diode and my last valve failed because one of them had failed. I didn't realise that was the problem until after I had changed it to an S plan. Now have changed it back to Y on boiler mfrs recommendation to avoid need for bypass. If the spindle turns easily you don't need to replace the entire valve, just the motor or head. There should never be a long term demand for heat or HW.this particular design of valve the synchronous motor is likely to burn out over time leading to nuisance replacements.