Now I have removed the suspected orange wire, and turn back power on from fuse box, but there is no light on the wilo pump, and I turn on my ideal boiler and it just stays at zero...

What have I done wrong? So far I have only removed the orange from box and open the housing of the two valves...
 

Attachments

  • 16816526299132332913211781509061.jpg
    16816526299132332913211781509061.jpg
    260.3 KB · Views: 45
So how may I probe at the orange wire at MV? I dont see any point that I can touch.
Apologies, there doesn’t appear to be a point you can touch, was thinking of a Drayton valve. Looks like you’ll have to do a live voltage test or remove the grey wire for the corresponding valve at wc and test between these, if you have continuity then it’s closed circuit and faulty.
 
You don't probe it at the m.valve, follow the black cable back to the junction box or wiring center, on of the wires fom the cable will be orange, remove it
 
There is a blue wire in that box which is a neutral, probe with red meter lead on the orange wire and the black meter cable on the terminal screw where the blue wire is, meter set to 500/600v AC.
 
There is a blue wire in that box which is a neutral, probe with red meter lead on the orange wire and the black meter cable on the terminal screw where the blue wire is, meter set to 500/600v AC.
I tried the above, got nothing, I don't seem to have any power even though I switched back from the fuse box...

You can see from the photo there is no green light on the wilo pump...

Is there any other switch in the system?
 

Attachments

  • 16816536370205417591088217794894.jpg
    16816536370205417591088217794894.jpg
    353.1 KB · Views: 43
There should be nothing on apart from power as we are trying to determine.ine if the end switch is still made on the suspect m valve
 
OK then that's your problem then, just confirm that the CH and HW are both off??
What?? It itself is a problem???

I have now connected the orange wire back and measured at WC between orange and blue/neutral or yellow/green earth, both showing 240v

And I did it with boiler on, program for both CH HW off.
 
Yes, that is the problem, IE your M.valve is still sending a signal to the boiler/pump to run even though he M valve isn't getting a demand to open from the relevant system so needs renewing, more than likely just the actuator which doesn't involve draining down the system.

Why didnt you probe between the removed orange wire and earth with power on but both CH & HW off, it should have read 230V.
 
Last edited:
I agree with you conclusion, but base on the fact that this lever is loose.

Still trying to understand how my system is not powered up without having it to reconnect back.

I am thinking to replace the synchron motor, which I have learnt how to from youtube, seems like an easy job, and yes, no draining system need, although it is a challenge for me as you may see from my earlier photos, the faulty one is the one below and i can't even remove the housing completely.

Did a quick search on google for price and availability, what would be the difference between the 20 quids one from screwfix and 10 quids one from amazon? which one is a safe/wise choice?

1681655991225.png
 
Have never replaced the motor only.

"Still trying to understand how my system is not powered up without having it to reconnect back."
If you mean boiler/pump not running then its because there is no demand because you had removed the orange wire from the faulty M.valve, if you leave it disconnected and create a CH or HW demand then the boiler/pump will start up, is it a CH or HW M.valve thats faulty?.
 
Yes, that is the problem, IE your M.valve is still sending a signal to the boiler/pump to run even though he M valve isn't getting a demand to open from the relevant system so needs renewing, more than likely just the actuator which doesn't involve draining down the system.

Why didnt you probe between the removed orange wire and earth with power on but both CH & HW off, it should have read 230V.
Sorry, I did that, so i did measure 240V between the removed orange and the earth/neutral, while the connected orange in the box are reading 0V.

I was too focusing on why I cant turn on the system even though i had turn power on...
 
  • Winner
Reactions: John.g
Have never replaced the motor only.

"Still trying to understand how my system is not powered up without having it to reconnect back."
If you mean boiler/pump not running then its because there is no demand because you had removed the orange wire from the faulty M.valve, if you leave it disconnected and create a CH or HW demand then the boiler/pump will start up, is it a CH or HW M.valve thats faulty?.
I get it now!!!!!

Thank you for being so patient to me!!!!!

Yes, I thought there were no power in the system, as I thought the green indicator on the pump means it is working/standby. I just disconnected the suspected orange wire again, turn on the system, boost hot water from the programmer to create demand, and boiler wakes up to work!
 
so I have swapped the synchron motor from a good one to the faulty one, it does not seem to help with the voltage, it still registers 240V.

So I need to replace the whole M. Valves?
 
so I have swapped the synchron motor from a good one to the faulty one, it does not seem to help with the voltage, it still registers 240V.

So I need to replace the whole M. Valves?
Yes, it’s not the motor at fault, it’s a microswitch.
 