Feb 14, 2016
74
6
8
Old setup.
Vented system - indirect
x2 Cold water tank in the loft. x2 80L Hot water tanks, regular boiler and stuart turner 4bar twin shower pump for the master bedroom shower. Worked pretty good, although the tanks were manky and old. The shower though was epic and used to blast water out. The house was gutted for refurbishment so plumber advised to change the set up for a new unvented system, that would deliver mains water pressure throughout the house. which it does.

New set up
Kingspan 300L horizontal tank. No shower pump and just the regular boiler. It’s all installed correctly, signed off and actually works quite well. All the taps and showers get mains water pressure.

Problem
I got too used to the shower pump pressure. The showerhead we have is an XL rainwater shower head and used to love the water blasting out. Whilst the showers still ok, it's just ok and not amazing anymore. If the shower in the family bathroom is run, there's a slight drop in pressure which i was expecting, but this makes the shower experience even less enjoyable.

Is there a solution?
We can’t install the same shower pump on the mains as it would draw too much water from the rest of the house and stop the other taps working - and probably mess with neighbours too. Assume this would also stop things like toilets refilling and draw air once water supply is exhausted.

So my questions are..... What is the solution for me to have a dedicated water supply for the shower again, so that I can use the pump?
Can I install a smaller vented system in addition to the unvented system that I have? The plumbers going to have a think on the best way of achieving this and let me know a price, but thought I’d ask on here too.

I know it’s potentially an expensive addition... but it just depends on cost. The shower is absolutely ok as it is, but i know how good it was and just wanted to make it awesome again.

Are there any other solutions that can be used with the new unvented tank I have?
 
To do that you'll need basically your old set up refitting just for that shower, then a way of heating a cylinder. If you're using a 4 bar pump, you'll be needing a decent size cylinder to supply this also....you're already in to a decent amount of cost to do that.

Seems madness to me. Are you not just being unrealistic about the performance of the shower? Surely if the cylinder has been fitted correctly and everything else is correct - Pipe sizing, filters clean, pressure, then you'll be getting more than a decent shower out of an Unvented HW system.

I almost agree with you here. He said its perfectly normal, but its just hard when you from from an awesome shower to an OK shower. as I said, perfectly happy with the other shower and taps, it's just think one becuase of the size of the head. As i've had high expections of the shower previously in comparision, i think im just a little underwhelmed. I might post clips from the performance before and after the install.

My plumber suggested somehting similar..... I was thinking if he does it for say £2-300 i'd probably do it, as at the moment, its acceptable with no other outlets on. I've not yet tested with with say a kitchen tap and the other shower, and the washing machine on and a toilet being flashed. I imagine it would drop a fair bit! I think 100L should do it as I had 2 80L tanks before and that was fine for a few showers.
 
I almost agree with you here. He said its perfectly normal, but its just hard when you from from an awesome shower to an OK shower. as I said, perfectly happy with the other shower and taps, it's just think one becuase of the size of the head. As i've had high expections of the shower previously in comparision, i think im just a little underwhelmed. I might post clips from the performance before and after the install.

My plumber suggested somehting similar... I was thinking if he does it for say £2-300 i'd probably do it, as at the moment, its acceptable with no other outlets on. I've not yet tested with with say a kitchen tap and the other shower, and the washing machine on and a toilet being flashed. I imagine it would drop a fair bit! I think 100L should do it as I had 2 80L tanks before and that was fine for a few showers.
Have you tried changing your shower head?
 
Fit a smaller size shower head and save the planet.
Useful response 🙂


For others- here are pics of the set up in the loft
 

Attachments

  • B100350B-91B0-48D7-ACEC-72D7FE0DA92C.jpeg
    B100350B-91B0-48D7-ACEC-72D7FE0DA92C.jpeg
    118.6 KB · Views: 80
  • B47AE349-50FA-49DF-8CAF-51E5F25C549C.jpeg
    B47AE349-50FA-49DF-8CAF-51E5F25C549C.jpeg
    124.3 KB · Views: 83
  • 65F55B49-7B6C-4FFE-90CA-0EA45D9CEBB0.jpeg
    65F55B49-7B6C-4FFE-90CA-0EA45D9CEBB0.jpeg
    133.6 KB · Views: 79
  • 8A2D0428-F040-4C89-B323-16683C87230C.jpeg
    8A2D0428-F040-4C89-B323-16683C87230C.jpeg
    124.4 KB · Views: 81
  • AE441A57-FD1D-425F-BA8F-666B118E0601.jpeg
    AE441A57-FD1D-425F-BA8F-666B118E0601.jpeg
    92.6 KB · Views: 86
Useful response 🙂


For others- here are pics of the set up in the loft
Well seeming the materials to do that will cost more than £2-300 I don't think you've got any chance there.

Can you see the size of the pipe incoming to the combination valve? (The one next to the white vessel which is brass colour). With all the insulation it's difficult to see pipe sizes.

But first off, it doesn't appear they've done balanced cold supplies. Which won't help.
 
Hey
Well seeming the materials to do that will cost more than £2-300 I don't think you've got any chance there.

Can you see the size of the pipe incoming to the combination valve? (The one next to the white vessel which is brass colour). With all the insulation it's difficult to see pipe sizes.

But first off, it doesn't appear they've done balanced cold supplies. Which won't help.

I’ll have a look again or ask the plumber when i can.

How can you tell it’s not balanced on the cold supplies?
 
Bit of an update as I've properly used both showers today simultaniously for the 1st time since the new set up was installed.

-Main shower on with nothing else on - was ok.
-2nd shower went on - pressure dropped a little as expectd- but still just about ok but little weak
-Toilet flushed and tap opened - water stopped flowing in both showers. mrs was NOT HAPPY as she was taking a shower haha.

I cant deal with that.

Spoken to the plumber in regards to a solution.
Appears that an accumulator, whilst ideal, wont work as the size of tank needed just wont be fit sensibily or logistically.

The suggestion is to re-install a pair water storage tanks back into the level 2 loft, and if i understand correctly will work in the following way:

-Both showers will be fed via the twin shower pump from cold tank level 2 and hot unvented cylinder on level 1.
-incoming mains supply will top up the cold tanks on level 2 as they empty
-hot water will be pumped from hot unvented cylinder for everywhere else using a 2nd sinlge pump that we used before (I think this is what he said but i might be wrong about that.)

How does this solution sound? He said this will effectly work as its a breaker tank. Just need to work out costs. I know it will be a bit but I dont really have a choice.

A little dissapointed tbh as I kind of wish I had just stuck with the original set up which did what it needed to do and fairly well. All the research I did and people I spoke to though suggested that the new unvented system was the way forwards..... cant help but feel like it was money wasted at the moment.

I aslo asked what the flow rate was and it was circa 13-15L per minute at the mains
 
What your plumber is suggesting is incorrect. You can't pump out of an unvented cylinder, you cannot also pump the cold from the tank and then have the hot supplied from the unvented.

He clearly doesn't know what he's doing, you need to get someone else in who can advise you much better.

As @ShaunCorbs says when need to know you incoming pressures, which you've been asked for a few times yet haven't provided them. You need to know these before you make any decision on what route to take.
 
  • Informative
Reactions: SJB060685
What’s your mains pressure ?

nothing open ?

one tap open ?

I cant remeber if i'm honest and I don't have a guage. However, as i've mentioned before, pressure at the taps is perfectrly fine at the moment, when the showers are not on.
[automerge]1577373831[/automerge]
What your plumber is suggesting is incorrect. You can't pump out of an unvented cylinder, you cannot also pump the cold from the tank and then have the hot supplied from the unvented.

He clearly doesn't know what he's doing, you need to get someone else in who can advise you much better.

As @ShaunCorbs says when need to know you incoming pressures, which you've been asked for a few times yet haven't provided them. You need to know these before you make any decision on what route to take.

I will try to get these readings.

As for what he's suggesting, i've only wrote what I think he think he said - i could be wrong.
 
This is what I was going to say Pork Chop. Plumbing is not my thing but I always believed no pumps on unvented and certainly not mains hot hot and boosted cold, how would they be balanced? If at all. As we all said the incoming mains pressure and flow rates is the first thing you check before considering mains hot water.
 
Before I comment further can a pump be used for hot water outlets on an unvented cylinder @ShaunCorbs?

not for the outlet but you can pump the supply to it eg break tank and pump if pressure is an issue

but it sounds like flow is the problem but until we get some figures we can’t say
 
  • Agree
Reactions: SJB060685
What your plumber is suggesting is incorrect. You can't pump out of an unvented cylinder, you cannot also pump the cold from the tank and then have the hot supplied from the unvented.

He clearly doesn't know what he's doing, you need to get someone else in who can advise you much better.

As @ShaunCorbs says when need to know you incoming pressures, which you've been asked for a few times yet haven't provided them. You need to know these before you make any decision on what route to take.

He told me it was measured at 1.6bar before he started the work. Not sure what it is now - need to re-measure when he is next here.
 
Ok when he’s here next week get him to fill this out

Pressure static (no outlets open eg just the pressure gauge open) is _______ bar
Pressure dynamic (one additional outlet open) is ______ bar
Flow static (one outlet open) is ______ Lpm
Dynamic (two outlets open) is ______ Lpm
 
1.6 bar is not good for unvented. As I said above, around that pressure you need a breaker tank and pumped mains with accumulator.

So his suggestion of 'making up' a breakter tank in loft level 2 is not an unsensible one?

In his defence he has not confirmed if this is what he is going to do but said he will look into it more for me and come up with the best solution based upon the space that I have.
[automerge]1577377492[/automerge]
Ok when he’s here next week get him to fill this out

Pressure static (no outlets open eg just the pressure gauge open)
Pressure dynamic (one additional outlet open)
Flow static (one outlet open)
Dynamic (two outlets open)

Sure - will do.
 