Appreciate the advice...

I have attached a schematic of my heating system. Has a 2018 Worcester boiler with a UVC (but the UVC could be older not sure when that was installed, I do know the previous Viessmann boiler had failed). There a couple of motorised valves for the heating and hot water.

The problem is that the pressure in the system (as read from 2 gauges on the pipe work) keeps falling (overnight 1.5bar to 1.2bar even with the boiler off and isolated).

So I have tried to isolate as best as I can and closed off gate valves to the rads (see picture) downstairs but I can see that given the position of the valves I can’t isolate the upstairs rads (unless I add a gate valve). But I can’t see any water from upstairs (the ceiling would have caved by now).

With the boiler off and isolated and the downstairs rads isolated the only thing that was on last night was the immersion heater in the tank. The heating control was on but could only have moved the motorised valve the boiler was off so nothing else. Was sure the leak was in the rads downstairs and so totally expected the pressure to have stayed at 1.5 as the rads were isolated but no, the pressure still fell.

The expansion tank has air (quick press of the Schrader valve).

None of the PRV drain lines have any water (bone dry).

There are two gauges (no idea why) but they both read the same so not a faulty gauge.

Is it possible the UVC is leaking? Can that ever happen... the mains pressure seems to be OK and I would have thought that the mains pressure (3 bar?) would prevent the heating coil (1.5 bar) from leaking?

Any suggestion for next steps? Should I drain the system and add the extra gate valve to isolate upstairs (even though I can’t believe it is that)?

All the tank/boiler valves are in the garage exposed so no chance of a leak being missed.

Really puzzled. Am hoping those with experience on UVC (I am not a plumber) can advise?
A0DDEC1C-5C40-4F56-A597-F94374456A67.jpeg
 
When you heating is on the pressure will increase say to 1.5 bar for the sake of this issue, when you heating is off the pressure will drop to its cold state say 1.2 bar this is quite normal. If your pressure continued to drop there would be another issue that would need investigating. Hope this helps.
 
When you heating is on the pressure will increase say to 1.5 bar for the sake of this issue, when you heating is off the pressure will drop to its cold state say 1.2 bar this is quite normal. If your pressure continued to drop there would be another issue that would need investigating. Hope this helps.


Thanks for the speedy response

i don’t think that’s it
When it’s cold I charge it to 1.5 bar. When it gets hot it goes up to 1.75ish.
When it cools it falls below 1.5.

Ive repeated this starting at 1.3 bar when cold (hoping that the leak might be small at a lower pressure). It goes up to 1.5/1.6 then again falls below 1.3 when cold.

If I leave it for longer it goes down to 1bar... I haven’t let it go below that.
 
Would suggest checking the EV pre charge air pressure, if this has been set too high then even the slightest change in temp will have a very big effect on the pressure as water is incompressible. When next the pressure falls to 1 bar, get a tyre pressure gauge and check the air end pressure, if that is > 1.0 bar, say 1.5 bar, then that just might be the problem and very easy to check without EV drain down.
Another clue to ~ 1.5 pre charge pressure is if it re pressurises almost instantly from 1.0 bar to 1.5 bar when topping up.
 
Last edited:
Can you isolate the under floor and check over night?
Yes I did that. Was surprised to see the pressure fall from 1.5 to 1.2 with the underfloor isolated overnight.

I had thought the leak was there but I guess not. The gate valves do work (as I had used them when the system was on and they did stop all the rads getting warm) so I don’t think the valves are letting by either.
[automerge]1586345644[/automerge]
Would suggest checking the EV pre charge air pressure, if this has been set too high then even the slightest change in temp will have a very big effect on the pressure as water is incompressible. When next the pressure falls to 1 bar, get a tyre pressure gauge and check the air end pressure, if that is > 1.0 bar, say 1.5 bar, then that just might be the problem and very easy to check without EV drain down.
Another clue to ~ 1.5 pre charge pressure is if it re pressurises almost instantly from 1.0 bar to 1.5 bar when topping up.
Oh... thanks ... good one. Will definitely do that.

I don’t have an isolation valve to the EV so I will wait for the pressure to get to 1bar and then check the EV and report back. I assume the pressure under the diaphragm should be the same as that above the diaphragm? Is that what you are saying?

Thanks!
 
What boiler do you have?
Any AAVs?
If you leave it for a few days does it continue to drop?

No other AAV other than the one that was in the boiler
— it’s a Worcester 40CDi Classic Regular


edit: Sorry need to add it does continue to fall if the system is running but I’ve never let it go below 1bar.
 
Last edited:
When was the boiler last serviced? Common problem is the AAV (automatic air vent/bleed) doesn't seal properly causing water to escape within the casing.
Ive also had a hairline crack inside the heat exchanger which was leaking down the condense pipe and loosing pressure.
have you had an engineer look into the issue?
 
If you isolated the underfloor and no leaks, and also the boiler with no leaks have you checked the expansion vessel, if its dropping while you are using the heating it should be easier to find. Have you looked at the pressure relief pipework outside?
 
If you isolated the underfloor and no leaks, and also the boiler with no leaks have you checked the expansion vessel, if its dropping while you are using the heating it should be easier to find. Have you looked at the pressure relief pipework outside?
Thanks for the suggestion.

Just to be clear I isolated the underfloor and the boiler from the pressure gauges but the pressure gauges still go down.

I agree there only seems to be the UVC and the EV (and the upstairs rads) that are now effectively linked to the pressure gauges. I’ve checked the EV by pressing the schrader valve (only for a second - is that enough?) and air came out. Is that the only test for an EV?

The PRVs (there is one near the EV and one at the UCV) are both in the garage (I know that’s against the regs (dodgy installer I guess) but the pipe terminates just above the floor /at the floor level). Both are bone dry... I did put a balloon on the end of the UCV PRV pipe even though there would be a wet patch on the garage floor and nothing has come out. The pressure is falling with everything switched off (ie no heating)

Any chance the UCV could be leaking internally? or is that physically not possible?
 
Last edited:
If you are loosing that amount of water and you have isolated the underfloor, by the way did you isolate the underfloor near the manifold? You have said there is no water from the PRV's pipework, you must by now have visible damp.
If you keep letting air out of the expansion vessel, you will have another problem. The expansion vessel will have a label with the amount of pressure that should be in the vessel, you might have to put some air in it. When the gauge is at the bottom or no reading pump air into the vessel to the manufactures guide on the label as you have an external expansion vessel it will possibly be more than you think so check the label.

Close all the radiator valves both ends and isolate the underfloor that would eliminate the radiators too and check overnight.
 
If you are loosing that amount of water and you have isolated the underfloor, by the way did you isolate the underfloor near the manifold? You have said there is no water from the PRV's pipework, you must by now have visible damp.
If you keep letting air out of the expansion vessel, you will have another problem. The expansion vessel will have a label with the amount of pressure that should be in the vessel, you might have to put some air in it. When the gauge is at the bottom or no reading pump air into the vessel to the manufactures guide on the label as you have an external expansion vessel it will possibly be more than you think so check the label.

Close all the radiator valves both ends and isolate the underfloor that would eliminate the radiators too and check overnight.

so the “underfloor” is just the central heating heating pipes under the screed there is not water UFH. There are two gate valves (flow and return) in the garage just before the pipes disappear into the wall and then into the screed of the kitchen on the other side of the wall. It’s just these two gate valves I have used to isolate the pipes in the screed (no manifold).

I agree for that much water loss I should see the water somewhere and I can’t. Driving me bananas...

so either:
1. The gate valves to the pipes in the screed are letting by and there is a leak under the screed... but when I ran the system hot with closed gate valves the small part of the pipes on the other side of the valve (before the wall) were not hot and none of the rads in kitchen were warm so I think the valves are OK
2, the valves to the boiler are letting by and there is a leak in the combustion chamber leaking into the condensate line... I am going close two more valves (above the pump (flow) and the magnafilter (return) just in case
3. One person here has indicated that the EV might be overcharged and so temperature is causing the issue (I’ll check the EV pressure). I don’t recall seeing a label but will take a better look in the morning. But I thought if the EV was the issue then I’d see water either at the schrader valve or the PRV ? Anywhere else to check?
4. I can add another gate valve to isolate the upstairs (and drop down rads) but if the leak was there then I’d have seen that water somewhere in the ceiling by now for sure if it was leaking that much.
5. The only thing left is the UVC - but Im not even sure that can leak internally?

Reallly appreciate the help!
 
Just to clarify re EV. (a bit long winded)

"Normal" would/could be a EV with a pre charge air pressure of 1.0 bar which is then pressurised (filling pressure) to 1.5 bar with system cold. A 12 litre EV at these conditions will then contain 2.4 litres of water (known as the reserve). Each time the system heats up then the expanded water will enter the EV and add to the 2.4 litres so the EV pressure will increase, example, a system of total vol 85 litres heated to average of (flow/return) 65C will expand and add a further 1.6 litres to the EV resulting in a final pressure of 1.98 bar. On cooling down, the EV pressure will reduce to its original 1.5 bar and its 2.4 litre water reserve. If there are any leaks in the system, then 2.4 litres (the reserve) will have to leak until the pressure falls to its pre charge pressure of 1.0 bar. Normally, with no leakage but allowing for occasional air venting, this reserve will last for at least a year (or even years) without top up.
Now, suppose the EV was pre charged to 1.5 bar and was prefilled to 1.5 bar then there is no water reserve and the final pressure after system heat up will be 1.87 bar and on cool down will be 1.5 bar but if there is even the tiniest of leaks then the pressure will fall very rapidly below 1.5 bar as there is no water reserve. That is why its so important and it's relatively easy to check that pre charge pressure.
 
  • Like
Reactions: Stigster
Just to clarify re EV. (a bit long winded)

"Normal" would/could be a EV with a pre charge air pressure of 1.0 bar which is then pressurised (filling pressure) to 1.5 bar with system cold. A 12 litre EV at these conditions will then contain 2.4 litres of water (known as the reserve). Each time the system heats up then the expanded water will enter the EV and add to the 2.4 litres so the EV pressure will increase, example, a system of total vol 85 litres heated to average of (flow/return) 65C will expand and add a further 1.6 litres to the EV resulting in a final pressure of 1.98 bar. On cooling down, the EV pressure will reduce to its original 1.5 bar and its 2.4 litre water reserve. If there are any leaks in the system, then 2.4 litres (the reserve) will have to leak until the pressure falls to its pre charge pressure of 1.0 bar. Normally, with no leakage but allowing for occasional air venting, this reserve will last for at least a year (or even years) without top up.
Now, suppose the EV was pre charged to 1.5 bar and was prefilled to 1.5 bar then there is no water reserve and the final pressure after system heat up will be 1.87 bar and on cool down will be 1.5 bar but if there is even the tiniest of leaks then the pressure will fall very rapidly below 1.5 bar as there is no water reserve. That is why its so important and it's relatively easy to check that pre charge pressure.
Thanks that explanation is quite helpful for me. I’ll let the system pressure fall away (or drain it) as i don’t have an iso valve to the EV and check it.
 
  • Like
Reactions: John.g
Yes, and as the pressure is decaying then check the air end pressure frequently and when (or if) the system pressure falls below the air end pressure then that will give you a very good indication of the air end pressure but would also advise checking both pressures at 1.5 bar or greater when hot just to ensure that both are equal. Also remember to take the differences in elevation between the EV and the system pressure gauge, if the EV is the lower (elevation) of the two then the air end pressure corrected to system pressure is air end pressure - 0.1bar for every 1M of elevation and +0.1bar if EV is the higher of the two.
 
Yes, and as the pressure is decaying then check the air end pressure frequently and when (or if) the system pressure falls below the air end pressure then that will give you a very good indication of the air end pressure but would also advise checking both pressures at 1.5 bar or greater when hot just to ensure that both are equal. Also remember to take the differences in elevation between the EV and the system pressure gauge, if the EV is the lower (elevation) of the two then the air end pressure corrected to system pressure is air end pressure - 0.1bar for every 1M of elevation and +0.1bar if EV is the higher of the two.
Thanks for the detailed responses.
The EV label says Precharge 1.5 bar.
The system is at 1.2 bar right now
I attached a tyre pressure gauge to the EV and it also reads 1.2 bar... hmmm not conclusive yet but possible little charge in the EV?

I will monitor both today/tonight (I might have to dump the system pressure to get the true reading in the EV)

the odd part then ... if the EV has no charge then the water must be going somewhere (or do I have that wrong?
If not out the PRV lines they are bone dry (the system has never gone to three bar and right now the system is cold and losing pressure)
 
Theoretically, if the precharge pressure fell to 0 Bar and with a filling pressure of 1.5 bar then the final pressure would be ~ 2.7 bar, close to PRV limit but I don't think you observed any pressures approaching this. If the precharge pressure was 1.5 bar originally and the system was filled to 1.5 bar then no reserve and frequent top ups. IMO, the precharge pressure should be 0.8/1.0 bar and fill pressure 1.3/1.5 bar to avoid excessive final pressure.
You will have to get a differential pressure of ~ 0.2/0.3 between EV/system pressure before you can get a good feel for the present EV pressure. Once you know that then you can see your next step(s).
 