Have emailed valiant about the hysteresis ( a new word I have learnt 👍 ) as everything is running nicely at CP1, would like to keep it there for at least a week, so I know I have somewhere to go back to 🤞 also at CP2 and especially CP3 the return temperature was rather high, non condensing. But will try next week.

You mentioned increasing the rad sizes so I came up with the following numbers based on that., I based them on doubling the rad outputs but can calculate it for any increase you want.
Based on your actual results it seems that you have a a relatively small installation with total rad output of ~ 9 kw.
If you look at the 9kw base below (top row) you can see that your actual output is 6.73kw with a return of 52C. If you were to increase (second row) the flow rate (CP2/CP3) to 0.63M3/hr to keep the boiler happy then by reducing the flow temp to 60C you will still get a return of 52C BUT a reduced output of 5.87kw, you would againthen need to up the flow temp on HW.

If you now doubled the rad outputs to 18kw, again with a happy boiler flowrate of ~ 0.6M3/hr, you can see the effect of different flow temps on rad output etc, if you select a flow temp of 60C then you will get a return of 44C and a output of 10kw, you would need to up the flow temp on HW.
If you select a flow temp of 72C then you will get a return of 52C and 14.35kw output and so on.

Table Below might be of some help.


Flow​
Return​
DeltaT​
Boiler​
Boiler​
Boiler​
Temp​
Temp​
Temp​
Output​
FlowRate​
FlowRate​
Deg rad​
Output​
Deg.C​
Deg.C​
Deg.C​
KW​
LPM​
M3/hr​
9KW Base​
40​
75%​
68​
52​
16​
6.73​
6.03​
0.36​
36​
65%​
60​
52​
8​
5.87​
10.52​
0.63​
18KW Base​
32​
56%​
60​
44​
16​
10.08​
9.03​
0.54​
38​
70%​
68​
48​
20​
12.60​
9.03​
0.54​
42​
80%​
72​
52​
20​
14.35​
10.28​
0.62​
 
  • Like
Reactions: Reddwarf4ever
You mentioned increasing the rad sizes so I came up with the following numbers based on that., I based them on doubling the rad outputs but can calculate it for any increase you want.
Based on your actual results it seems that you have a a relatively small installation with total rad output of ~ 9 kw.
If you look at the 9kw base below (top row) you can see that your actual output is 6.73kw with a return of 52C. If you were to increase (second row) the flow rate (CP2/CP3) to 0.63M3/hr to keep the boiler happy then by reducing the flow temp to 60C you will still get a return of 52C BUT a reduced output of 5.87kw, you would againthen need to up the flow temp on HW.

If you now doubled the rad outputs to 18kw, again with a happy boiler flowrate of ~ 0.6M3/hr, you can see the effect of different flow temps on rad output etc, if you select a flow temp of 60C then you will get a return of 44C and a output of 10kw, you would need to up the flow temp on HW.
If you select a flow temp of 72C then you will get a return of 52C and 14.35kw output and so on.

Table Below might be of some help.


Flow​
Return​
DeltaT​
Boiler​
Boiler​
Boiler​
Temp​
Temp​
Temp​
Output​
FlowRate​
FlowRate​
Deg rad​
Output​
Deg.C​
Deg.C​
Deg.C​
KW​
LPM​
M3/hr​
9KW Base​
40​
75%​
68​
52​
16​
6.73​
6.03​
0.36​
36​
65%​
60​
52​
8​
5.87​
10.52​
0.63​
18KW Base​
32​
56%​
60​
44​
16​
10.08​
9.03​
0.54​
38​
70%​
68​
48​
20​
12.60​
9.03​
0.54​
42​
80%​
72​
52​
20​
14.35​
10.28​
0.62​
Thanks that’s defo given me something to think about and work on....currently I a, using CP1 @7KW inlet 53oC & flow temperature 66oC the house is slowly heating up, I set the HW to come on 2 hours before the heating goes off at 10pm and 3 hours in the morning when the heating goes on at 7am....this achieved 47oC at the cylinder stat, which I know is around 60oC at the outlet, unfortunately although the boiler modulates really well, every so often, 1-2 hours it cuts out, I can only assume ( don’t suppose these boilers have an event log 🤞 ), that it’s over temperature maybe it climbs to 69oC if a TRV changes up or down, I suppose 🤔 if it had a 5oC tolerance instead of 3oC maybe it would manage.....when it cuts out, I set the flow temperature to 85oC ( max ) when the gas firing starts reducing again, the temperature drops to 60-65oC & i then set the flow temperature back to 66oC and it starts modulating again.....will try the other ideas soon.....

thanks
 
If the TRVs are of the manual type, like mine, they should give pretty good modulating control as against on/off even though they have a very small hysteresis (in Air) of 1 to 2C, also when setting up I find that even a difference of 0.2/0.3 on the index makes a big difference to the room temperature, all of mine (8) are set to between 1.8 and 2.2 to give ~ 18C to 22C room temperature and with a boiler flow temp of ~70C (OF boiler, cutin/cutout 75C/65C) quite regularly give return temps as low as 40C, oil fired boilers have no problems in dealing with very high deltaTs and even though they run flat out all the time and are constantly cycling, the 20/25 litre heat exchanger acts as a buffer so no cut on flow temp cut out on firing up.
I have read of some on/off and other control problems with the programmable TRVs.
 
Thanks that’s defo given me something to think about and work on....currently I a, using CP1 @7KW inlet 53oC & flow temperature 66oC the house is slowly heating up, I set the HW to come on 2 hours before the heating goes off at 10pm and 3 hours in the morning when the heating goes on at 7am....this achieved 47oC at the cylinder stat, which I know is around 60oC at the outlet, unfortunately although the boiler modulates really well, every so often, 1-2 hours it cuts out, I can only assume ( don’t suppose these boilers have an event log 🤞 ), that it’s over temperature maybe it climbs to 69oC if a TRV changes up or down, I suppose 🤔 if it had a 5oC tolerance instead of 3oC maybe it would manage..when it cuts out, I set the flow temperature to 85oC ( max ) when the gas firing starts reducing again, the temperature drops to 60-65oC & i then set the flow temperature back to 66oC and it starts modulating again..will try the other ideas soon.***.

thanks
Even though I would be surprised if any of the TRVs are doing much controlling with the house not fully heated, it is possible, and if so, to help avoiding this annoying 2 hourly cut out you might consider changing to PP2, this, by my calculation, should give you very close to the present performance on CP1 but may well help to smoothen out the flowrate if these TRVs are inclined to hunt.
 
  • Like
Reactions: Reddwarf4ever
Thanks John, currently I am running the Boiler at 66oC, @7KW with a typical return temperature of 52-53oC. It’s modulating very well & the house does get up to 22.5oC ( I actually set the room stat to 23.5oC during 7am to 10am & and the boiler goes off, which allows the rads to cool down and improve the return temperature when the boiler restarts) I set the heating to come on at 7am which goes off at 10pm. Have set Hot water to come on at 7am to 10am & 8pm to 10pm this manages to keep the Hot water at a good temperature, also it heats the water while the heating is on & in condensing mode. If I increase the pump pressure / flow and have to lower the flow temperature, I will have problems with Hot water heating. Don’t have separate controls and settings for heating and hot water and would be ***bersome to keep changing the boiler flow temperature.

I will try PP2 and see how that performs
 
  • Like
Reactions: John.g
Thanks John, currently I am running the Boiler at 66oC, @7KW with a typical return temperature of 52-53oC. It’s modulating very well & the house does get up to 22.5oC ( I actually set the room stat to 23.5oC during 7am to 10am & and the boiler goes off, which allows the rads to cool down and improve the return temperature when the boiler restarts) I set the heating to come on at 7am which goes off at 10pm. Have set Hot water to come on at 7am to 10am & 8pm to 10pm this manages to keep the Hot water at a good temperature, also it heats the water while the heating is on & in condensing mode. If I increase the pump pressure / flow and have to lower the flow temperature, I will have problems with Hot water heating. Don’t have separate controls and settings for heating and hot water and would be ***bersome to keep changing the boiler flow temperature.

I will try PP2 and see how that performs
For some reason the pagelayout using safari has got reallybad, is in Columns tried Firefox and ok, wonder if can be fixed? Looks like all the adverts causing it
 

Attachments

  • B75437EE-2B39-4554-9B96-299CC5D5E9BD.png
    B75437EE-2B39-4554-9B96-299CC5D5E9BD.png
    419.9 KB · Views: 43
I just go back to new posts to display the full page or something like that.
 
Oddly enough, the webpages are displaying ok today open safari, must depend on which adverts are running 🤔 the DAB 3 evosta pump I received did NOT have the foam insulation shroud that I saw in a YouTube installation video and assumed it would be included any thoughts ?
 

Attachments

  • 13896966-7159-4844-839C-4B29EB86F2BE.jpeg
    13896966-7159-4844-839C-4B29EB86F2BE.jpeg
    17.5 KB · Views: 43
Just had a reply from DAB, despite it showing this pump with the insulating shroud, all over their website, apparently it’s not on the model I bought, even though it’s a DAB 3 and can’t be bought separately.....although another online retailer said I can buy it for £29 + VAT plus £4 delivery, quite expensive for a piece of foam 🤯 will use my hessian wrap from the old pump, not so pretty but effective.....don’t see why DAB couldn’t just send me one out......
 

Attachments

  • 72A0D3EC-F114-444C-A6D7-69E1574E9932.png
    72A0D3EC-F114-444C-A6D7-69E1574E9932.png
    2.4 MB · Views: 39
  • 078CCAE1-BDF7-4B6E-BCA8-83425D06FC6B.png
    078CCAE1-BDF7-4B6E-BCA8-83425D06FC6B.png
    1 MB · Views: 46
  • 03E4D2A3-728D-480F-93E2-4E9D6F80EEF7.png
    03E4D2A3-728D-480F-93E2-4E9D6F80EEF7.png
    2.1 MB · Views: 53
  • 08A0840E-A93B-4FB9-8AD9-4CBCD0443DD5.png
    08A0840E-A93B-4FB9-8AD9-4CBCD0443DD5.png
    2.4 MB · Views: 46
  • B11CEF71-1B00-4BF9-94AA-32C339F3CB22.jpeg
    B11CEF71-1B00-4BF9-94AA-32C339F3CB22.jpeg
    17.5 KB · Views: 42
  • Like
Reactions: John.g
I tried PP2, but the boiler seemed to be cutting out more, not sure if fluctuations upsetting it, as it only has a +3oC Flow to Actual tolerance, maybe this is the reason, still waiting for Vailant to respond about if it should be +5oC 🤔 trying CP2 at the moment, has been behaving very well on CP1, but one radiator only barely gets warm, it’s in a downstairs extension room, maybe it’s a plumbing problem 🤯 but on CP3 it certainly got hot....

thanks
 
The reason the rad is not circulating is probably that CP1 is limited to a 1.8M head which realistically is a bit low, CP2 at 3M should be a good compromise to get circulation, theoretically, at least, the flow rate should increase from 0.4 m3.hr to 0.52 M3/hr and you may be able to nurse another few kw from the boiler without cut out. CP3 at 4.5M is probably the best choice, hydraulically, you may loose a few % in boiler efficiency but maybe a small price to pay for comfortable heating until Vaillant respond.
 
Last edited:
The reason the rad is not circulating is probably that CP1 is limited to a 1.8M head which realistically is a bit low, CP2 at 3M should be a good compromise to get circulation, theoretically, at least, the flow rate should increase from 0.4 m3.hr to 0.52 M3/hr and you may be able to nurse another few kw from the boiler without cut out. CP3 at 4.5M is probably the best choice, hydraulically, you may loose a few % in boiler efficiency but maybe a small price to pay for comfortable heating until Vaillant respond.
Thank you CP2 did work reasonably well, the ‘ problem rad ‘ began to warm up. I then switched to CP3 and the ‘ problem rad ‘ is now very hot, can still keep my hand on it just....the other rads are really hot, the one next to my Wife’s chair is too hot too touch, with the Boiler flow set at 64oC however the return temperature has now increased to 56oC 🔥 Might leave it at CP2, where the return was 51-53oC 🥶 the ‘ problem Rad ‘ is not so important, as it’s in the ‘ ‘game room’ not used very much. Probably need a CP 2 1/2 🤔, since increasing the flow from CP1 to CP2 and more recently CP3 the boiler is modulating a lot better, hasn’t cut out at all yet. Also the Hot water heated from 7am-11am & 8pm to 10pm is working very well, with CP1 & 2, Will be a different story in the Summer months when it will be Hot Water only.....
 
Thank you CP2 did work reasonably well, the ‘ problem rad ‘ began to warm up. I then switched to CP3 and the ‘ problem rad ‘ is now very hot, can still keep my hand on it just....the other rads are really hot, the one next to my Wife’s chair is too hot too touch, with the Boiler flow set at 64oC however the return temperature has now increased to 56oC 🔥 Might leave it at CP2, where the return was 51-53oC 🥶 the ‘ problem Rad ‘ is not so important, as it’s in the ‘ ‘game room’ not used very much. Probably need a CP 2 1/2 🤔, since increasing the flow from CP1 to CP2 and more recently CP3 the boiler is modulating a lot better, hasn’t cut out at all yet. Also the Hot water heated from 7am-11am & 8pm to 10pm is working very well, with CP1 & 2, Will be a different story in the Summer months when it will be Hot Water only.***.
What was/is the pump head and flow on CP2 & CP3? , theoretically PP3 should give somewhere in the middle, by my calculations, but your numbers will tell us more.
 
CP1 10W 1.8m 0.4m3/hr
CP2 17W 3.0m 0.7m3/hr
CP3 30W 4.5m 0.9m3/hr
PP3 26W 4.1m 0.8/m3/hr - 0.9m3/hr

CP3 gives a good flow, all rads very hot, but inlet temperature >55oC
CP2 All rads hot except one, which is warm, inlet temperature 52-53oC
CP1 all rads hot except one barely warm, inlet temperature 52-53oC

trying PP3

believe the flow is a ‘ calculated’ one, can’t see how they could fit a flow meter inside the pump....with pump head and watts it’s an easy calculation.

DAB going to send me a ‘ spare’ heat shroud they found. They say the manual and website is for the European model not the UK one....how I am supposed to know that is beyond me.....think for the few pence it costs, all their pumps should have this....

thanks
 
CP2, CP3 & PP3 are doing as I would have expected.
The pump actually only uses the power and pump+motor efficiency to calculate the head and flowrate, it knows which mode/head is selected and can then derive the actual head/flowrate, the clever part IMO is how it derives the pump+motor efficiency for every single point on all the curves. Some hold that it is only a approximation especially on some of the UPS models and it may well be but before I installed my Wilo Yonos Pico, I just connected it up to a a gravity feed with a gate valve on the discharge and measured the flowrates for a number of different operating modes and it seemed to be within 5 to 10% of what the pump curves showed for the displayed power consumptions, (I don't have head & flowrate displayed.), so all in all a good aid to navigation IMO. You can also estimate it (the flowrate) from the (clamped) boiler output and deltaT.
 