Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

System or Combi in local pub?

View the thread, titled "System or Combi in local pub?" which is posted in Central Heating Forum on UK Plumbers Forums.

Irrespective of the rad sizes, if they are not getting hot then no room heat.
You say 40mm piping, a system with a 42kw boiler with a rad dT of 12C will require a flow rate of 50LPM, 3.0M3/Hr, even if all the rads were located at the very end of a 50M run (100M total) the pipe friction losses are ~ 3M, a 8M pump will flow 50LPM @ a 6M head and assuming the boiler pump is similar to a UPS3, this pump will flow 50LPM @ a 2.8M head, maybe be worth looking at the boiler hx loss at a flow of 50 LPM, also condition of 40mm piping.

To clarify, the extra 25/80 pump has been installed in the heat output line from the boiler so
it sucks from the boiler pump? Does that sound stupid? The boiler pump and the new pump send the pressure to the two zones via the 42mm pipework in the loft down to the rads below. I think that there was always a problem with the Concorde Boiler in getting the furthest rads hot.
 
To clarify, the extra 25/80 pump has been installed in the heat output line from the boiler so
it sucks from the boiler pump? Does that sound stupid? The boiler pump and the new pump send the pressure to the two zones via the 42mm pipework in the loft down to the rads below. I think that there was always a problem with the Concorde Boiler in getting the furthest rads hot.
The pumps as you describe are in series and this can cause a number of problems. Some means of separation is needed and I explained what that is in an above comment.
There’s only so much we can advise you through a website on a phone or laptop etc and we have. You need to contact several reputable firms both qualified and experienced in these scenarios and explain your problem and the advise you’ve had here.
 
To clarify, the extra 25/80 pump has been installed in the heat output line from the boiler so
it sucks from the boiler pump? Does that sound stupid? The boiler pump and the new pump send the pressure to the two zones via the 42mm pipework in the loft down to the rads below. I think that there was always a problem with the Concorde Boiler in getting the furthest rads hot.

Its certainly unconventional but I'd venture that there are systems with pumps installed like this and working OK, as pointed out above, two different head pumps in "series" may cause one to fight the other, they are really not in series in accepted pump jargon where both pumps are installed one immediately behind the other, but generally one would then install one pump with the required head.
In your case, the boiler circ pump pumps from the return, through the boiler Hx and then supplies the 8M pump.
I would suggest trying to establish what the flow rate is from other data to hand, the boiler flow and return temps and the boiler output, is all you need but these three values arn't often available from the boiler display but the flow/return temps can be measured on the pipes which will give some info at any rate, the boiler output is more difficult but if both zones are open then maybe can get a good idea. If that 8m pump displays its power in watts? (W) then flow rate can be derived exactly, from the pump curves.
 
Thank you for all the responses. They are waiting for a Navien engineer to attend to replace
the heat exchanger under guarantee? Why does that need replacing?
In the meantime the boiler pressure can only be supplied if the cold water pressure supply is
being balanced by the pressure valve constantly sending cold water supply to the outflow
resulting in hundreds of gallons being wasted every day. I thought it was a local offence
to waste water? it is the only way he can get heating in the pub.
What a mess.
 
Are you saying that the Boiler PRV (safety valve) is lifting at 3 bar and discharging water which then has to be replaced with cold water?
 
Are you now saying the plate heat exchanger for HW has failed and the PRV is lifting?
If so then yes you will be losing water but hundreds of gallons a day I highly doubt.
This seems to be getting worse and worse. You need a reputable engineer to go over the whole system. I’m not going to read or comment on this thread further. We’ve given you the advice you need, you now need to get someone out who actually knows a thing or two.
 
Are you saying that the Boiler PRV (safety valve) is lifting at 3 bar and discharging water which then has to be replaced with cold water?
Yes, stupid isn't it! They are going to replace the heat exchanger so it seems. Several seals have burst causing water leaks since installation. What mess. I find it difficult to accept the inept performance and lack of knowledge from the installers.
 
Do you absolutely know that the "bursting" seals are on the central heating side ?, strange, because if so, the boiler PRV, in lifting at 3bar, should prevent just such a occurance, if the problem is coming from the DHW side then it would mean a extremely high mains pressure which hasn't a pressure reducing valve (PRV) installed.
 
Its certainly unconventional but I'd venture that there are systems with pumps installed like this and working OK, as pointed out above, two different head pumps in "series" may cause one to fight the other, they are really not in series in accepted pump jargon where both pumps are installed one immediately behind the other, but generally one would then install one pump with the required head.
In your case, the boiler circ pump pumps from the return, through the boiler Hx and then supplies the 8M pump.
I would suggest trying to establish what the flow rate is from other data to hand, the boiler flow and return temps and the boiler output, is all you need but these three values arn't often available from the boiler display but the flow/return temps can be measured on the pipes which will give some info at any rate, the boiler output is more difficult but if both zones are open then maybe can get a good idea. If that 8m pump displays its power in watts? (W) then flow rate can be derived exactly, from the pump curves.
Thank you for all your input. It is appreciated. The system is still under performing. Now waiting for Navien engineers assessment of the situation. This should not be so when the customer has spent £3000 with professionals?
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "System or Combi in local pub?" which is posted in Central Heating Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
JohnHuson,
Last reply from
EvilDrPorkChop,
Replies
47
Views
4,252
Back
Top