Hi Guys,
I went to service a Worcester Greenstar 37cdi combi boiler for a customer today and I checked the inlet pressure on the boiler whilst running in chimney sweep mode. The Inlet pressure was only 15mb and I checked the mi's and it says the boiler should'nt be commissioned if the pressure is less that 18mb. The boiler seems to be working fine and the anaylser readings are ok but I have capped of the gas supply to the boiler for now as im not sure how to catergorise it? Is it At Risk? Are the in any danger if they continue to use it? There is a 22mm gas supply to the boiler probably about 16m with bends etc included.The property is empty at the moment and the customer wants to let it out. Any ideas guys, is the only answer to install 28mm gas pipe?
Thanks Guys
I went to service a Worcester Greenstar 37cdi combi boiler for a customer today and I checked the inlet pressure on the boiler whilst running in chimney sweep mode. The Inlet pressure was only 15mb and I checked the mi's and it says the boiler should'nt be commissioned if the pressure is less that 18mb. The boiler seems to be working fine and the anaylser readings are ok but I have capped of the gas supply to the boiler for now as im not sure how to catergorise it? Is it At Risk? Are the in any danger if they continue to use it? There is a 22mm gas supply to the boiler probably about 16m with bends etc included.The property is empty at the moment and the customer wants to let it out. Any ideas guys, is the only answer to install 28mm gas pipe?