vern spoke to WB this afternoon and was sent a PDF of their recommended system install plan using their LLH. i have attached this PDF. On page 11 of this PDF it shows a full system diagram of how to hookup this LLH.
From what you described earlier about distribution to the underfloor heating manifolds on the secondary flow and return; as i mentioned earlier i have 3 heating manifolds and all the ports on the LLH on the secondary side would be used on the 2 branches for the first 2 manifolds (ground floor and first floor), so how would i connect the 3rd (last) manifold (the loft rooms) using this WB low loss header?
Also since each underfloor heating manifold has a circulating heat pump on its own corresponding manifold can i omit the heating pump in this WB plan just before their Radiators are, i.e where the corresponding new underfloor heating manifolds will be situated? oh no just realised you can't attach the PDF as it is too big a file 🙁 i hope you know what i mean though 🙂
I will keep it brief as you really need someone on site!
Option 1.......If you use WB LLH you can common the upstairs and loft F&R's just run the circs to the upstairs UFH manifold and tee off to the loft UFH manifold, 28mm should do it, BUT i dont know the load or length of runs.
No you need a pump from the secondary's to the UFH manifolds the manifold pumps only circ through UFH pipe and mixing valve due to resistance, you also need a pump for each boiler on the primary's making 5 pumps (1 for each boiler =2,.......1 for each manifold=2 as up and loft are common'ed up..... 1 x DHW coil on megaflo........ + 1 bronze for DHW secondary re circs making 9 as you have 3 already on the UFH manifolds built in!!!
Option 2.......Use a broag LLH header which has 2 x 1" primary's for 2 boilers and 1 x "2" secondary's come off in 54mm or 42mm copper with reducing tees as needed for 3 x UFH manifolds and 1 dhw ..Totals pumps 10 as above + 1 pump for loft maifold as it would be not common'ed up to upstairs!
Option 3 ......Junk the 24 Ri ,bash in a 40 CDi (actually 41KW) no LLH Commercial spec grunfos pump for primary's say 42mm copper so 11/2" flanged, 4 zone valves (DHW,1 for each UFH Manifold) with autobypass honeywell DU146........5 pumps = 1 x main 1 x bronze secondary 3 already fitted on UFH manifolds, ensure megflo has a balancing valve fiited on return from coil, to obtain 20 deg diff, as 1/1/2" pump will send it through the coil too quickly on DHW mode only, Autobypass will sort the rest, and UFH manfiolds will look after themselves due to mixing valve etc...........
Aww Cr@p book me a hotel!!!!